The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by ghost307
Today at 06:25 AM
International Wire Colour Codes
by Tjia1981
Yesterday at 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 257 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#42304 - 09/18/04 05:04 PM 15A receptacle
RobbieD Offline

Registered: 02/23/03
Posts: 238
Loc: Canada
I have a 15A breaker supplying a 15A 120V receptacle. I have a power tool plugged into the receptacle and it draws 13A. It occasionally trips the breaker on start-up or when it is loaded down. I am planning to change the breaker to 20A. The wire is good for this but my question is- Do I have to change the duplex receptacle to a 20A 120V also? I think that I do because the receptacle would be able to provide more than 15A. Am I right? Thanks!

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#42305 - 09/18/04 05:40 PM Re: 15A receptacle
PCBelarge Offline

Registered: 06/08/03
Posts: 657
Loc: Dobbs Ferry, NY, USA
If this breaker is supplying a single receptacle, than the receptacle has to be rated the same as the branch circuit that supplies it (210.21(B)(1).

210.21(B)(3) Table - shows that a 15 ampere rated receptacle can be supplied by a 20 ampere circuit. Provided there is more than one receptacle on that circuit.

Remember that a 20 ampere circuit requires a 12 AWG conductor. See 240.4(D).


[This message has been edited by PCBelarge (edited 09-18-2004).]
Pierre Belarge

#42306 - 09/18/04 05:45 PM Re: 15A receptacle
Electric Ian Offline

Registered: 02/10/04
Posts: 132
Loc: MA, USA
Single Receptacle on an Individual Branch Circuit.
A single receptacle installed on an individual branch circuit shall have an ampere rating not less than that of the branch circuit.

#42307 - 09/18/04 06:09 PM Re: 15A receptacle
Electric Eagle Offline

Registered: 04/20/02
Posts: 928
Loc: Alpharetta, GA
If the 15amp receptacle is a duplex, it is considered 2 receptacles and is allowed on a 20 amp circuit.

#42308 - 09/18/04 07:29 PM Re: 15A receptacle
russ m Offline

Registered: 02/22/03
Posts: 165
Loc: Burbank,IL,USA
210.21 would require the use of a 20amp device.

I guess this answer is just redundant.

[This message has been edited by russ m (edited 09-18-2004).]

#42309 - 09/18/04 10:38 PM Re: 15A receptacle
frank Offline

Registered: 05/29/01
Posts: 361
Loc: windsor ontario canada
According to my CCS inspector the receptical must be rated for the breaker size.Started in the 98 code book i think.A T-slot recpiical rated at 20 amps is the only device they allow here in Ontario and its all you can do if you want to use 15a rated equipment on a 20a circuit.This is for Canada and i knew from the question you were another Canuk. Also at 80% rating 12 amps is the max allowable current draw on a 15 amp breaker according to code so the tool should be factory wired with 20A cord cap if its CSA.

[This message has been edited by frank (edited 09-19-2004).]

#42310 - 09/19/04 07:35 AM Re: 15A receptacle
Active 1 Offline

Registered: 02/22/03
Posts: 684
Loc: Grayslake IL, USA
It was my understanding that 210-21 refers to a SINGLE receptical not a DUPLEX receptical. Single = 1 receptical, duplex = 2 recepticals. I guess it is also a local interpitation thing.

I'm for 20A recepticalss on all 20A circuits. I would spend the extra $1 or so because you are getting a better device.


#42311 - 09/19/04 07:40 AM Re: 15A receptacle
RobbieD Offline

Registered: 02/23/03
Posts: 238
Loc: Canada
Thanks guys! I will replace the breaker and receptacle both will be 20A.

#42312 - 09/19/04 08:07 AM Re: 15A receptacle
CJS Offline

Registered: 09/16/04
Posts: 35
Loc: Sanford,NC, USA
One more thing (I don't know if anyone said this or not):

Your max load on a 15A circuit is 80% or 12A. If you exceed that, the breaker will likely trip (or even if you get close to 12A).
Your max load on a 20A crkt is 16Amps.

This is a general rule and some exceptions can apply.

What you are doing is providing 125% for continuos duty (longer than 3 hours) and also you are building in a safety precaution by only going 80% as required in art. 220.

Anything at or near 12A requires a 20A circuit.

#42313 - 09/19/04 09:24 AM Re: 15A receptacle
Ron Offline

Registered: 03/13/02
Posts: 577
Loc: White Plains, NY
CJS, a good reference to backup your theory is 210.23(A)(1)