#42232 - 09/17/04 05:18 AM fill factor in a box
tomselectrc Offline
Member
Registered: 03/14/04
Posts: 49
Loc: warren mi us
do'es a gfi plug change the fill factor in a box
Top
Work Gear for Electricians and the Trades
#42233 - 09/17/04 06:18 AM Re: fill factor in a box
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1374
Loc: West Jordan, Utah, USA
No. Each yoke or strap counts as two conductors, regardless of its physical size.
_________________________
Ryan Jackson,
Salt Lake City
Top
#42234 - 09/17/04 06:09 PM Re: fill factor in a box
CTwireman Offline
Member
Registered: 02/07/02
Posts: 840
Loc: Connecticut, USA
It is always a wise idea to use a deep box for GFIs, dimmers, etc.

I wonder why the code doesn't address the extra space that GFIs take up??

Peter
_________________________
Peter
Top
#42235 - 09/17/04 06:38 PM Re: fill factor in a box
Jacuzzi Guy Electric Offline
Member
Registered: 10/25/02
Posts: 33
Loc: Dearborn Heights Michigan Unit...
If the box is too small. Theres is always the GFI Breaker. No space problems there
Top
#42236 - 09/17/04 11:19 PM Re: fill factor in a box
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
GFCI breaker.

Higher cost, more likely to trip from cumulative leakage currents and you have to go find it if it trips.

I will stick with a GFCI outlets in deep boxes at the point of use.

The majority of our prints require GFCI outlets at each location that needs GFCI protection.

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#42237 - 09/18/04 08:05 AM Re: fill factor in a box
CJS Offline
Member
Registered: 09/16/04
Posts: 35
Loc: Sanford,NC, USA
Yeah, that's the other thing: GFI's in standard boxes.
It's a good idea to use a larger box but not mandatory. Most of us will learn by experience in this regard because you will often have a ground fault after cramming all of that into the box!

We don't need the NEC to dictate our every move do we? That book keeps getting thicker & thicker as it is...

Anyone who has ever installed a GFI receptacle in a standard sized weather-proof box knows that if you have more than one cable entering the box you will have one helluva time getting that receptacle into the box. And so you add a weather-proof extension ring and you're good to go.
Same with an indoor box: Use a 20.5 cu. in. or even a 22 cu. in. if you have more than one romex to contend with. You'll be glad you do at trim-out.

:~)
Top

Member Spotlight
Member Since: 01/22/05
Posts: 5316
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 95 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals