The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
Texas_Ranger 8
sparkyinak 8
Potseal 6
Who's Online
2 registered (crselectric, mbhydro), 232 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#42028 - 09/15/04 12:32 PM Poco clearances
velect Offline
Member

Registered: 05/01/04
Posts: 79
Loc: st joseph mi usa
What kind of clearance must a power company have with their primary lines to a residential roof?

Also what height must they maintain off the ground with primary power?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#42029 - 09/15/04 01:09 PM Re: Poco clearances
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
velect,
It depends on the voltage, the type of wire involved (Insulated vs Un-insulated) and also the type of roof.
Sag under high temperatures also comes into the calculation.
Also, it depends upon whether the area (roof) can be stood on or not.
Not that it will be much help NZECP34 gives Bare wires of -650V - 3.7metres above the peak of the roof.
+650V - 5.0mtrs. Sorry I can't be of more help.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#42030 - 09/15/04 01:38 PM Re: Poco clearances
CharlieE Offline
Member

Registered: 04/23/04
Posts: 204
Loc: Indianapolis
Velect, Trumpy's absolutely correct. You need a lot more information to answer that question. Exactly what is the problem that is prompting this question? Have you contacted the serving electric utility? I am assuming these are electric utility wires and the NESC covers the installation.

You actually need the location in the span, the length of the span, the attachment heights at both poles, the low point of the sag, and the temperature when measured just to calculate the blowout and maximum sag under hot weather loading or winter ice (whichever is worse).

If the wires are actually over the house, all the same information is needed as well as the height of the roof where the wires pass over, the type of roof so to ascertain whether it is accessible by pedestrians (by the NESC rules, forget the definition of accessible in the NEC for this application).

Trumpy did a good job of answering your question but you really need the services of the serving electric utility's trained engineer who is familiar with the NESC or his company's standards since they are based on the NESC and will either meet or exceed the Code.

- - - - - - - - - - - - - - - - - - - - - - - - - - -
Charlie Eldridge, Indianapolis, Utility Power Guy
_________________________
Charlie Eldridge, Indianapolis Utility Power Guy

Top
#42031 - 09/15/04 06:20 PM Re: Poco clearances
velect Offline
Member

Registered: 05/01/04
Posts: 79
Loc: st joseph mi usa
Wires are uninsulated.....7200 volt.
Eave of the roof is 11 feet from one of the phases
A local roofer was electrocuted Friday when he was moving a shingle conveyor (lifts bundles on the roof) and hit one of the phases. The house is two story with a 4/12 pitch

The three phase feeds a lumber yard a few hundred yards down the road.
Poles are approximately 200 feet apart

[This message has been edited by velect (edited 09-16-2004).]

Top
#42032 - 09/16/04 05:32 AM Re: Poco clearances
CharlieE Offline
Member

Registered: 04/23/04
Posts: 204
Loc: Indianapolis
The standard required clearance is 7.5 feet for 12470Y/7200 volts. I don't understand why this would not be enough clearance for normal conditions. If any maintenance is to be done, it would be time to call the electric utility and have them de-energize the line or cover it. Our policy is to de-energize since people seem to think that the line is safe if it is covered (it is not, it is just safer).

I am really sorry for the fatality but you can't walk out into traffic and expect not to get hit.
_________________________
Charlie Eldridge, Indianapolis Utility Power Guy

Top



ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals