Not exactly electrical, but from past experience an air conditioner (heat pump) will not turn back on right away after it is shut off. There is a 2 min or so delay to protect the compressor. While checking the power to one today it would go on and off immediately with the breaker. Is this possibly normal on dfferent units?

Also the customer said the condenser fan motor would shut off while the compressor still ran at times? This doesn't seem right either.
_________________________
The Golden Rule - "The man with the gold makes the rule"
Top
Work Gear for Electricians and the Trades
#41800 - 09/09/04 03:04 PM Re: A/C Question
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
It could be normal or low on refrigerant.

On smaller AC units it is a thermal overload that trips out when you try to do a quick restart. This happens because the gas pressure against the piston will not allow the motor to turn crating a locked rotor condition.

On larger units there is an actual timer to prevent short cycling.

[This message has been edited by iwire (edited 09-09-2004).]
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#41801 - 09/09/04 05:02 PM Re: A/C Question
twh Offline
Member
Registered: 03/11/04
Posts: 901
Loc: Regina, Sask.
I don't think I've seen a compressor run without the condenser - at least on an air conditioner.
Top
#41802 - 09/09/04 05:16 PM Re: A/C Question
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
If the condenser is equipped for running in low ambient temperatures it may cycle or even be speed controlled.

Or you may just have a bad condenser fan motor that is cycling on the thermal protection. If that is what is happening the compressor will usually kick off shortly after.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#41803 - 09/09/04 05:20 PM Re: A/C Question
electricman2 Offline
Member
Registered: 11/09/03
Posts: 269
Loc: Thomasville, NC USA
If it is a heat pump it is normal for the condenser fan to shut off and the compressor remain on when in the defrost cycle in the heating mode. If not a heat pump possibly the thermal overload in the fan motor is opening for some reason.
Sometimes the 2 minute or so delay is in the thermostat so opening and closing the circuit breaker would start and stop unit with no delay.
_________________________
John
Top
#41804 - 09/09/04 09:41 PM Re: A/C Question
aldav53 Offline
Member
Registered: 08/22/01
Posts: 545
Loc: Chandler, AZ USA
electricman,
It is a heat pump, but the defrost cycle is not needed because it is still in the cooling mode until it reverses for winter in the heat mode.
Good point on that delay being in the thermostat, thats probably it.
The customers original complaint was that the A/C breaker trips 7 or 8 times a day and an A/C guy check it and said it was ok.
Its still hot here in AZ so it runs a lot still.
_________________________
The Golden Rule - "The man with the gold makes the rule"
Top
#41805 - 09/10/04 02:48 AM Re: A/C Question
maintenanceguy Offline
Member
Registered: 12/02/01
Posts: 300
Loc: Southern NJ, USA
Some ac/s have delay on break timers that start timing when electric is turned off, some have delay on make timers that start counting when electricity is turned on. Most residential ac/s don't have any timers at all.

And some ac/s (heat pumps too) have a condenser fan that cycles on and off to maintain a constant condenser coil temperature. The fan runs less often on a cool day than it does on a hot day. If so, the common wire to the fan motor would go through a pressure switch located somewhere on copper lines going to the condenser coil.
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 40 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals