#41767 - 09/08/04 04:08 AM exhaust hoods...
cavo148 Offline
Member
Registered: 01/19/04
Posts: 79
Loc: New Jersey
How are commercial exhaust hoods wired for control where there's one unit for exhaust and another for incoming fresh air. Would the on/off switch be wired for them to come on at the same time or switched seperately? BTW, the one I'm looking at has a 3/4 HP exhaust and a 1/3 HP return motor. Thanks in advance.
Andy
Top
Work Gear for Electricians and the Trades
#41768 - 09/08/04 07:56 AM Re: exhaust hoods...
Anonymous
Unregistered

Andy, I usually set a control cabinet or control the motor starters / relays with a separate 120v control circuit to pull in the starter coils at the same time with one switch. In my area the incoming air is usually heated depending on outside temp as well so there is another coil.

Here is the rub. Most Fire Dept Inspectors in my area want the makeup air shut off and the Exaust Hood to start in any alarm condition in the space. You can drive a separate relay using aux power and alarm contacts in the FACP or have the FACP drive a control module if it's addressable.
I have a control drawing I could send as a JPEG file if you would like.
Top
#41769 - 09/08/04 04:23 PM Re: exhaust hoods...
twh Offline
Member
Registered: 03/11/04
Posts: 901
Loc: Regina, Sask.
I thought the exhaust should not run without the make-up, because the exhaust alone can draw air down the chimney. I think the commercial make-up air units have an air proving switch, that locks out the exhaust.
Top
#41770 - 09/09/04 06:41 AM Re: exhaust hoods...
earlydean Offline
Member
Registered: 12/22/03
Posts: 751
Loc: Griswold, CT, USA
And, for best comfort we want a slight positive pressure at all times to ensure minimal loss of unconditioned air.
_________________________
Earl
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
2 registered (Admin, sparkyinak), 74 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals