The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by twh
Today at 06:28 AM
On Delay Relay with Auto Reset
by Potseal
Yesterday at 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
2 registered (jraef, LongRunner), 188 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#41767 - 09/08/04 04:08 AM exhaust hoods...
cavo148 Offline
Member

Registered: 01/19/04
Posts: 79
Loc: New Jersey
How are commercial exhaust hoods wired for control where there's one unit for exhaust and another for incoming fresh air. Would the on/off switch be wired for them to come on at the same time or switched seperately? BTW, the one I'm looking at has a 3/4 HP exhaust and a 1/3 HP return motor. Thanks in advance.
Andy

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#41768 - 09/08/04 07:56 AM Re: exhaust hoods...
Anonymous
Unregistered


Andy, I usually set a control cabinet or control the motor starters / relays with a separate 120v control circuit to pull in the starter coils at the same time with one switch. In my area the incoming air is usually heated depending on outside temp as well so there is another coil.

Here is the rub. Most Fire Dept Inspectors in my area want the makeup air shut off and the Exaust Hood to start in any alarm condition in the space. You can drive a separate relay using aux power and alarm contacts in the FACP or have the FACP drive a control module if it's addressable.
I have a control drawing I could send as a JPEG file if you would like.

Top
#41769 - 09/08/04 04:23 PM Re: exhaust hoods...
twh Offline
Member

Registered: 03/11/04
Posts: 898
Loc: Regina, Sask.
I thought the exhaust should not run without the make-up, because the exhaust alone can draw air down the chimney. I think the commercial make-up air units have an air proving switch, that locks out the exhaust.

Top
#41770 - 09/09/04 06:41 AM Re: exhaust hoods...
earlydean Offline
Member

Registered: 12/22/03
Posts: 749
Loc: Griswold, CT, USA
And, for best comfort we want a slight positive pressure at all times to ensure minimal loss of unconditioned air.