The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 340 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#41637 - 09/03/04 08:35 AM Remote Gazebo
SJT Offline

Registered: 07/24/02
Posts: 242
We have a Gazebo (concrete slab approx. 50x20) to wire that will have few lights and receptacles. It will be used for people to have parties, BBQS, etc. To stay code compliant, is it OK to run 2 - 20 amp ckts. out to the structure, or do I have to install a 2ckt. sub-panel at the structure. All sides are open on this patio and the breaker panel that I will run the ckts. from is approx. 50' away. I was going to go with a sub- panel, and another Elec. said I did not need it. Thanks for the input.

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#41638 - 09/03/04 08:51 AM Re: Remote Gazebo
amp-man Offline

Registered: 06/23/01
Posts: 144
Loc: Sacto, California US of A
If you run a multi-wire circuit (i.e., an Edison ckt--two hots off diff. legs & a neutral), there's no need for a subpanel. And of course you need an equipment grounding conductor. So some 12/3 wg UF will do the trick, or bk, red, wht, grn THHW in pipe.


#41639 - 09/03/04 10:07 AM Re: Remote Gazebo
SJT Offline

Registered: 07/24/02
Posts: 242
I plan on running seperate nuetrals. One ckt. for the lights, one for the outlets. When I was going through the code, in the ground section with diffrent buildings, structures, etc., I was getting into the panel idea, but it sounds like it's not required.

#41640 - 09/03/04 11:02 AM Re: Remote Gazebo
iwire Offline

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
I strongly suggest the use of the multiwire branch circuit as amp man suggested, it is better for voltage drop.

Also one multiwire branch circuit will not require a ground rod to be driven at the Gazebo. If you run two - 2 wire circuits you must drive a ground rod and connect it to the EGC at the gazebo. 250.32(A) be sure to read the exception.

You will also need disconnects at the gazebo for the circuits you run out there. 225.31

This could be one double pole switch or two single pole switches.

Good Luck, Bob