#41635 - 09/02/04 08:26 PM Zinsco 40*C Breaker
PEdoubleNIZZLE Offline
Member
Registered: 06/16/04
Posts: 176
Loc: McKeesport, PA, USA
I have an old Zinsco panel in my house with type Q breakers (not for long, will be replaced with a Murray 200A panel). It was there when I moved it, it has a 100A, then a 100A Breaker going to a sub panel. The one going to the sub says 40 degrees C. Table 310.16 only goes down to 60C. I'm just wondering what size copper wire would be used on 100A 40*C. The breaker has #2 SE cable with a #4 Neutral connected to it, which I know is illegal because 310.15 doesn't apply here.
P.S. Sorry if I used some incorrect terms, I'm an engineering student, not an electrician.
Thanks!
Top
Work Gear for Electricians and the Trades
#41636 - 09/02/04 11:18 PM Re: Zinsco 40*C Breaker
caselec Offline
Member
Registered: 04/14/02
Posts: 558
Loc: San Jose, CA
40C is the ambient temperature (average enclosure temperature) the breaker is calibrated for.
_________________________
Curt Swartz
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 55 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals