The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
1 registered (sparkyinak), 122 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#41635 - 09/02/04 08:26 PM Zinsco 40*C Breaker
PEdoubleNIZZLE Offline
Member

Registered: 06/16/04
Posts: 176
Loc: McKeesport, PA, USA
I have an old Zinsco panel in my house with type Q breakers (not for long, will be replaced with a Murray 200A panel). It was there when I moved it, it has a 100A, then a 100A Breaker going to a sub panel. The one going to the sub says 40 degrees C. Table 310.16 only goes down to 60C. I'm just wondering what size copper wire would be used on 100A 40*C. The breaker has #2 SE cable with a #4 Neutral connected to it, which I know is illegal because 310.15 doesn't apply here.
P.S. Sorry if I used some incorrect terms, I'm an engineering student, not an electrician.
Thanks!

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#41636 - 09/02/04 11:18 PM Re: Zinsco 40*C Breaker
caselec Offline
Member

Registered: 04/14/02
Posts: 557
Loc: San Jose, CA
40C is the ambient temperature (average enclosure temperature) the breaker is calibrated for.