The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Forum Software Upgrade coming soon...
by gfretwell
01/17/17 01:16 PM
Why cables look like they do
by Texas_Ranger
01/17/17 12:33 PM
Re: Fabricating Guards out of Lexan?
by ghost307
01/17/17 11:21 AM
Would ELV branch circuits be a good idea?
by ghost307
01/17/17 11:18 AM
100% breakers?
by Texas_Ranger
01/16/17 06:13 AM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
HotLine1 19
Webmaster 14
Trumpy 12
ghost307 12
gfretwell 10
Who's Online
2 registered (ghost307, gfretwell), 0 Guests and 78 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#41509 - 08/29/04 11:56 AM 700A Main Breaker nuisance tripping
mgd001 Offline
Junior Member

Registered: 08/29/04
Posts: 5
Loc: Santa Rita, GU usa
Hi, this is my first post, happy to be on this forum.

The main breaker for our 3-phase/460v building power tripped on Friday and the Emergency Generator and ATS switched on. I noticed that the Genset out put display showed this: 468 v ,60hz , 715 amps total.

but each seperate phase measured around 235amps. is this enough to trip the breaker due to overloading?

I thought that a breaker marked 700 amps could hold 700 amps per pole?

thanks to all.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#41510 - 08/29/04 12:39 PM Re: 700A Main Breaker nuisance tripping
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
I am a little confused with how many amps you are drawing, I have never seen a generator with a "Total Amps" meter.

If you have 235 amps per phase then we would say the breaker has a 235 amp load.

Each pole of a 700 amp breaker is rated 700 amps but we do not call it a 2100 amp breaker.

A typical 700 amp breaker should not be loaded to more than 80% (560 amps per leg) for periods exceeding 3 hours. That is unless you have a 100% rated breaker, most are not.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#41511 - 08/29/04 02:10 PM Re: 700A Main Breaker nuisance tripping
mgd001 Offline
Junior Member

Registered: 08/29/04
Posts: 5
Loc: Santa Rita, GU usa
The amps draw per leg was around 235 each. a=235amps, b=235amps, c=235amps

Thanks for the clarification.

Our Generator was installed a few weeks ago and it has a slick microprocessor display, with the Total amps reading.

This 700 amp breaker has a little switch assembly Called a "ground-censor" on the panel below the breaker that could be sensing a fault somewhere.

I'll post more details soon.