The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Correct rotation, wrong sequence
by Potseal
Today at 03:14 PM
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
HotLine1 10
Potseal 9
sparkyinak 8
Texas_Ranger 7
Who's Online
0 registered (), 215 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#41288 - 08/24/04 01:14 PM 100 amp panel
jayson Offline
Member

Registered: 05/12/04
Posts: 49
Loc: russellspringsky
in a house panel with a 100 amp main can u put a 100 amp breaker on the bus . like if in the panel i have 2 20 amp lighting circuit breakers and 30 amp and 50 amp range and a 100 amp below that feeding central air unit.any help would be aprecicated thanks

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#41289 - 08/24/04 01:23 PM Re: 100 amp panel
cpalm1 Offline
Member

Registered: 01/06/04
Posts: 62
you should not have a 100 amp breaker on the A/C it should be 20, 30, or 40 amps depending on the A/C units rating

Top
#41290 - 08/24/04 05:18 PM Re: 100 amp panel
e57 Offline
Member

Registered: 05/27/03
Posts: 2837
Loc: S.F.,CA USA
60A tops if the thing (AC) is a real beast, sounds sketchy?
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason

Top
#41291 - 08/24/04 05:36 PM Re: 100 amp panel
Dave55 Offline
Member

Registered: 05/08/04
Posts: 666
Loc: Crystal Lake, Illinois, USA
Typically, the wire is sized to the load, and the breaker matches the wire size. There are other circumstances, of course. What is the air conditioning load, and the wire gauge?

Dave55

Top
#41292 - 08/24/04 06:47 PM Re: 100 amp panel
Electric Eagle Offline
Member

Registered: 04/20/02
Posts: 928
Loc: Alpharetta, GA
It is posible to have a 100 breaker for A/C, it's very common around here to have a 100 amp breaker serving a disconnect for 3 or 4 A/C units rather than having 3 or 4 diferent home runs for each unit.

To answer the guy's original question, yes it is posible, but if the A/C's draws a combined load anywhere near that 100 amps, it's too much for the panel with all the olther stuff.

Top
#41293 - 08/24/04 07:16 PM Re: 100 amp panel
jayson Offline
Member

Registered: 05/12/04
Posts: 49
Loc: russellspringsky
the 100 amp breaker is feeding a diconnnect with a 60 amp breaker.

Top
#41294 - 08/25/04 06:36 AM Re: 100 amp panel
Geno Offline
Member

Registered: 08/27/01
Posts: 16
Loc: Syracuse, NY USA
What size is the wire?

Top
#41295 - 09/03/04 11:53 AM Re: 100 amp panel
SJT Offline
Member

Registered: 07/24/02
Posts: 242
Loc: PATCHOGUE, N.Y.
Do you have a range and a dryer on this panel also? It sounds like you need to upgrade to a 200 amp service. Things would be OK, but then the 60 amp load of the AC arrives on the scene.
Very possible the main could trip. Is it worth living with that chance?