The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Yesterday at 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 218 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#41282 - 08/24/04 07:02 AM Upgrading service in a 2 family house
pspetrone Offline
Junior Member

Registered: 08/23/04
Posts: 3
Loc: Middletown, CT, USA
I have a two part question regarding upgrading the existing 60 amp electrical service in my home. First, some background.
1. It is a 2 family home in Connecticut
2. Heat, hot water and ranges are all gas
3. it is being sold as a condition of the sale is upgrading the services to seperate 200 amp services.

First question is, considering that heat, hot water and ranges are all gas, would 100 amp services be sufficient for roughly 860 sq. ft apartments, considering that the new owner may install central air and an air compressor in the garage to do remodelling work?
Second, Is there a way to have a 200 amp service brought in and split at the meter can to provide seperate 200 amp services to each apartment or do I have to bring in a 400 amp service from the street and split it at the meters to provide the 200 amp services to each apartment?

Any help would be GREATLY appreciated since I need to get this done ASAP!!!!!

Thanks

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#41283 - 08/24/04 11:57 AM Re: Upgrading service in a 2 family house
earlydean Offline
Member

Registered: 12/22/03
Posts: 749
Loc: Griswold, CT, USA
Yes, Yes and NO.
_________________________
Earl

Top
#41284 - 08/24/04 12:07 PM Re: Upgrading service in a 2 family house
pspetrone Offline
Junior Member

Registered: 08/23/04
Posts: 3
Loc: Middletown, CT, USA
So this means that YES, 100 amp services for each apartment would be enough, even for central air and an air compressor and YES, I can split a 200 amp feed at the meter (I'm assuming just wiring the meters in parallel???. I ask because I didn't know if that was legal to do)and NO, I don't need to try and bring a 400 amp service into the house from the street. is that right? Thanks

Top
#41285 - 08/24/04 12:48 PM Re: Upgrading service in a 2 family house
earlydean Offline
Member

Registered: 12/22/03
Posts: 749
Loc: Griswold, CT, USA
Yes
_________________________
Earl

Top
#41286 - 08/24/04 01:34 PM Re: Upgrading service in a 2 family house
SteveMc Offline
Member

Registered: 02/05/04
Posts: 61
Loc: Rock Hill, SC
earlydean, you do ramble on sometimes, try to keep your answers short next time.

Top
#41287 - 08/24/04 05:00 PM Re: Upgrading service in a 2 family house
earlydean Offline
Member

Registered: 12/22/03
Posts: 749
Loc: Griswold, CT, USA
OK
_________________________
Earl

Top