#40677 - 07/31/04 06:01 AM gfi & afi problems
derater Offline
Member
Registered: 03/30/02
Posts: 179
1)In an old duplex a lot of existing circuit feeds are 12-3.I used one of them for kitchen
counter receptacles;the problem is when using a GFI tester both GFI'S pop.Is this usual, legal; is because of shared nuetral?
2)AFI similar problem-I think previous sparky
tied noodles in attic JB;result is that one or the other AFI will hold, but turning 2nd
AFI kicks off the first one; will shared nuetral do this ?
Top
Work Gear for Electricians and the Trades
#40678 - 07/31/04 07:58 AM Re: gfi & afi problems
necbuff Offline
Member
Registered: 07/08/04
Posts: 41
Loc: Lebanon Tn USA
You can not share a neutral on the LOAD side of these devices. A fault is sensed thru the neutral, a split return path. If you are using a shared neutral on these circuits you can pigtail each neutral to the device and you should be fine. You can share on the line side. These devices are "blind" on the line side. All would be legal but only one will work!
_________________________
Kenny Wilee
Top
#40679 - 08/02/04 03:10 PM Re: gfi & afi problems
trekkie76 Offline
Member
Registered: 06/19/04
Posts: 220
Loc: baileyville, maine, usa
I have noticed that using split circuits on arc fault breakers will do as you are describing. The breaker is "seeing " an imbalance, which it will on the split circuit, and trips.
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6775
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 87 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals