The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
Trumpy 8
sparkyinak 7
Who's Online
0 registered (), 81 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#40677 - 07/31/04 06:01 AM gfi & afi problems
derater Offline
Member

Registered: 03/30/02
Posts: 182
1)In an old duplex a lot of existing circuit feeds are 12-3.I used one of them for kitchen
counter receptacles;the problem is when using a GFI tester both GFI'S pop.Is this usual, legal; is because of shared nuetral?
2)AFI similar problem-I think previous sparky
tied noodles in attic JB;result is that one or the other AFI will hold, but turning 2nd
AFI kicks off the first one; will shared nuetral do this ?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#40678 - 07/31/04 07:58 AM Re: gfi & afi problems
necbuff Offline
Member

Registered: 07/08/04
Posts: 27
Loc: Lebanon Tn USA
You can not share a neutral on the LOAD side of these devices. A fault is sensed thru the neutral, a split return path. If you are using a shared neutral on these circuits you can pigtail each neutral to the device and you should be fine. You can share on the line side. These devices are "blind" on the line side. All would be legal but only one will work!
_________________________
Kenny Wilee

Top
#40679 - 08/02/04 03:10 PM Re: gfi & afi problems
trekkie76 Offline
Member

Registered: 06/19/04
Posts: 219
Loc: baileyville, maine, usa
I have noticed that using split circuits on arc fault breakers will do as you are describing. The breaker is "seeing " an imbalance, which it will on the split circuit, and trips.