The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
22 minutes 4 seconds ago
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
sparkyinak 9
Texas_Ranger 8
Potseal 6
Who's Online
2 registered (LongRunner, sparkyinak), 94 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 3 1 2 3 >
Topic Options
Rate This Topic
#4063 - 09/09/01 10:42 AM AFCI breakers
pauluk Offline
Member

Registered: 08/11/01
Posts: 7693
Loc: Norfolk, England
I've been reading some of your older messages about provision of AFCIs. This is quite fascinating as we don't have anything like these breakers over here (not yet anyway!).

Does anyone know exactly how these devices work?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#4064 - 09/09/01 05:29 PM Re: AFCI breakers
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
http://www.zlan.com/arc.htm

Paul;
they sense an arc of (i believe) 75W or more

.......have you ever heard the expression 'tail waggin' the dog'???


[This message has been edited by sparky (edited 09-09-2001).]

Top
#4065 - 09/10/01 05:17 AM Re: AFCI breakers
pauluk Offline
Member

Registered: 08/11/01
Posts: 7693
Loc: Norfolk, England
Thanks for the link. I figured they'd obviously have to be more complex than the standard thermal/magnetic or even amplified GFI types.

The only way I can see for them to work is for the circuitry to look for short pulses of increased current but not trip on longer pulses. I can see how such a circuit could be developed with simple op-amps etc. in integrated form, though I wouldn't be surprised if they actually use a micro-controller to analyze the current pulses.

I just wondered if any more technical details on the actual arrangement were available.

Does the AFI rely on the control circuitry to trip on normal overcurrent, or does it incorporate a normal thermal/magnetic trip as a backup?

 Quote:
Originally posted by sparky:

.......have you ever heard the expression 'tail waggin' the dog'???


Most definitely!

Top
#4066 - 09/10/01 03:14 PM Re: AFCI breakers
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
http://www.zlan.com/afci_c4.htm

Paul,
i could'nt really answer any of your Q's , this (check pix in link) is definitly not my forte' .

i'd like to know how to detect a bad AFCI

Top
#4067 - 09/10/01 05:09 PM Re: AFCI breakers
sparky66wv Offline
Member

Registered: 11/17/00
Posts: 2339
Loc: West Virginia
Steve,

No "test button" as per GFCI?

I've yet to get a close look at one of these buggers...

Guess the "pair of wires and a really steady hand" won't do it...

Great Q... Just how do we test them?



I suppose one could run a spot (read arc) light on an AFCI circuit (If you could find one that runs on 120V 20A) and provide a known safe long-lasting arc...

[This message has been edited by sparky66wv (edited 09-10-2001).]
_________________________
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI

Top
#4068 - 09/11/01 02:27 AM Re: AFCI breakers
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
Virgil;
yes there's a test button on the breaker itself, just like a GFI. I just haven't found a tester to plug in thoughout the circuit like the one's used for receptacles with the GFI tester.
where would i get a calculated arc of say, 76watts's

Top
#4069 - 09/11/01 01:53 PM Re: AFCI breakers
nesparky Offline
Member

Registered: 06/21/01
Posts: 650
Loc: omaha,ne
Don't worry since this will be a problem sure the mahufacturers who got the code comitte to cram them down our throuts will soon have a expensive tester for us to buy.
_________________________
ed

Top
#4070 - 09/11/01 03:55 PM Re: AFCI breakers
pauluk Offline
Member

Registered: 08/11/01
Posts: 7693
Loc: Norfolk, England
 Quote:
Originally posted by sparky66wv:

I've yet to get a close look at one of these buggers.


Now there's another word that has a somewhat different meaning on this side of the Atlantic!

Top
#4071 - 09/11/01 04:01 PM Re: AFCI breakers
pauluk Offline
Member

Registered: 08/11/01
Posts: 7693
Loc: Norfolk, England
 Quote:
Originally posted by sparky:
http://www.zlan.com/afci_c4.htm
Paul,
i could'nt really answer any of your Q's , this (check pix in link) is definitly not my forte' .
i'd like to know how to detect a bad AFCI


Thanks for that. The diagrams & notes on that site are very helpful. Looks as though as I was right about the microprocessor analyzing the current.

Did you follow the links there to the pages about testing an AFCI?

They seem to be using another micro-driven test unit which stores typical arc waveforms and then re-generates them to test the breaker, except it's done via the non-shunted neutral line only in order to keep the current down.

Top
#4072 - 09/11/01 05:07 PM Re: AFCI breakers
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
http://www.zlan.com/testing/testing3.htm

well it certainly looks $$$$

Top