The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Correct rotation, wrong sequence
by Potseal
Today at 03:14 PM
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
New in the Gallery:
12.5A through 0.75mm≤ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
HotLine1 10
Potseal 9
sparkyinak 8
Texas_Ranger 7
Who's Online
0 registered (), 218 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#40570 - 07/26/04 06:30 PM 3 -phase sub-panel
Attic Rat Offline
Member

Registered: 12/14/03
Posts: 530
Loc: Bergen Co.,N.J. USA
...Had an emergency call to a diner I do alot of work in,for an intermittently tripping breaker.Went to check it out,and the 20a.Square"D" tandem breaker was HOT to the touch.The breaker governs a refrigerator compressor and drew only 14.3amps.@ 120 volts,...still,the darn thing was hot.The system voltage is 120/208,and the sub-panel feeder is 200amps.I changed the breaker,rearranged the order so that I could put the compressor on it's own 20amp.,HACR rated breaker...Haven't heard from them since,...this was last Saturday.What could've been the problem?? A faulty breaker,??When it did trip,it went to "overload" status,by which,I mean tripped in the middle position,if it had been a short,or a locked rotor,the breaker would've tripped all the way off,...no??
At 14.3 amps,I can't see why it behaved that way...I'm baffled...Could an unbalanced panel load cause this??
I'm all out of theories!! HELP!!
Russ

[This message has been edited by Attic Rat (edited 07-26-2004).]
_________________________
.."if it ain't fixed,don't break it...call a Licensed Electrician"

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#40571 - 07/26/04 06:37 PM Re: 3 -phase sub-panel
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Russ,
The most common reason for "hot" breakers is a poor connection. It can be at the buss, the load conductor or even inside of the breaker itself.
Don
_________________________
Don(resqcapt19)

Top
#40572 - 07/26/04 06:44 PM Re: 3 -phase sub-panel
Bjarney Offline
Moderator

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
Increased contact resistance in the breaker pole will manifest as excess heat from additional I²r loss. It may be too late to determine if the breaker has been taken out of service, but in-situ AC millivolt-drop tests can sometimes flush out the problem. See http://ecmweb.com/mag/electric_testing_contact_quality/index.html

Also, with a little care‚ÄĒsimilar measurements can be made at the wire/load-side connection and main bus/breaker line-side spring-clip connection.




[This message has been edited by Bjarney (edited 07-26-2004).]

Top
#40573 - 07/26/04 07:48 PM Re: 3 -phase sub-panel
caselec Offline
Member

Registered: 04/14/02
Posts: 557
Loc: San Jose, CA
I agree with Don and BJ. If the connection to the buss and to the branch wire was good it is probably bad contacts in the breaker. The trip position is the same for both thermal and magnetic.
_________________________
Curt Swartz

Top
#40574 - 07/27/04 02:30 AM Re: 3 -phase sub-panel
KevInMA Offline
Junior Member

Registered: 07/23/04
Posts: 5
Loc: Seekonk, MA
Russ, also, short circuit or overload, the breaker always trips to the middle position.

Top
#40575 - 07/27/04 06:53 AM Re: 3 -phase sub-panel
JBD Offline
Member

Registered: 07/12/01
Posts: 599
Loc: WI, USA
How hot is hot?

The hottest spot of a circuit breaker is the operating handle.

Looking in a 1987 version of NEMA AB-1.
[The] Temperature-rise of various materials and parts;
Main operating means: (b) parts of insulating material - 60C [140F]
Main circuit terminals for external connections - 50C [122F].

Note: the handle rating is based on a temperature rise (increase) above an ambient of 25C (77F).

So even a properly functioning breaker, that is fully loaded, can be too hot to touch.

Top
#40576 - 07/27/04 03:21 PM Re: 3 -phase sub-panel
aland Offline
Member

Registered: 05/20/04
Posts: 187
Loc: United Kingdom
Russ, How about position of the breaker in relation to other loaded breakers, are you getting any heat transfer that is causing the tripping problem? You did say that you have rearranged the order, could the new position be cooler? Just a thought.
Good Luck.
Alan

Top
#40577 - 07/27/04 04:15 PM Re: 3 -phase sub-panel
capt al Offline
Member

Registered: 06/20/04
Posts: 203
Loc: Norton, Ma USA
Russ, I agree with BJ and Don. Look at the link BJ provoided. I use the millivolt drop test on breakers all the time. Readings approaching 100 mv toss the breaker and install a new one. This is one of the tests I do when doing Infarred work for my company.

Alan is also correct. Other loads around the tripping breaker can cause overheating.

Al

Top
#40578 - 07/27/04 07:43 PM Re: 3 -phase sub-panel
Attic Rat Offline
Member

Registered: 12/14/03
Posts: 530
Loc: Bergen Co.,N.J. USA
... Thanx all,...as usual,you guys were right there for me...JBD,the breaker was HOT,...and I believe that's what contributed to the tripping..Also,the surrounding breaker(s)could've been a heat factor as well...it definetly stopped tripping once I changed the breaker from a tandem to a single pole QO breaker,and relocated it in the panel..The case of the faulty breaker was melted a bit,and the sticker was singed..
I firmly believe that it was the breaker whose contacts may have been carbonized,and contact was poor... Thanx again guys,I'll keep you posted if anything else crops up..
Russ



[This message has been edited by Attic Rat (edited 07-27-2004).]
_________________________
.."if it ain't fixed,don't break it...call a Licensed Electrician"

Top
#40579 - 07/28/04 06:45 AM Re: 3 -phase sub-panel
JBD Offline
Member

Registered: 07/12/01
Posts: 599
Loc: WI, USA
Russ,

I agree the breaker probably needed to be replaced. And definitely, the initial panel layout was poor. Remember the ambient air (actually the inside of the panel) around any one breaker needs to be below 25C (77F) or you will reduce it's current carrying capability.

My point was, the temperature of the breaker is not a major factor in troubleshooting a circuit. The behavior of the circuit is more important. If the breaker tripped whenever the compressor kicked in, then it was tripping magnetically. If it tripped after a few minutes of running then it was tripping on overload.

Square D QO breakers only have three positions On, Tripped, and Off. You can not tell what kind of event caused a QO breaker to trip.