The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Would ELV branch circuits be a good idea?
by Texas_Ranger
24 minutes 10 seconds ago
100% breakers?
by Texas_Ranger
28 minutes 26 seconds ago
Forum Software Upgrade coming soon...
by Trumpy
01/14/17 07:11 PM
Faricating Guards out if Lexan?
by Trumpy
01/14/17 07:09 PM
Dangerous DIY Advice
by Potseal
01/12/17 09:52 AM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
HotLine1 15
gfretwell 11
ghost307 10
sparkyinak 10
Trumpy 8
Who's Online
2 registered (LongRunner, Texas_Ranger), 288 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#40440 - 07/20/04 04:01 AM 3 wire sub panel
derater Offline
Member

Registered: 03/30/02
Posts: 182
Cust.,who is also a builder I work for, wants a sub panel in detached garage via the 3 wire he alresdy has; should I drive a ground rod there?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#40441 - 07/20/04 06:02 AM Re: 3 wire sub panel
watthead Offline
Member

Registered: 10/13/01
Posts: 182
Loc: South Carolina
Yes, but you should only use the three wire method if there is, and will be, no other metallic paths between the two structures. This includes metal water or gas pipe, telephone or other wires. If you have no other metal connection you should drive a rod or two per requirements, and bond to neutral like service equipment.

Top
#40442 - 07/20/04 12:00 PM Re: 3 wire sub panel
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Great advice from Watthead, the code section that you need to read would be 250.32(B)(2)

Also no matter if you run a separate EGC or not out to a detached building you must connect grounding electrodes to the panel grounding bar.

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#40443 - 07/20/04 01:19 PM Re: 3 wire sub panel
derater Offline
Member

Registered: 03/30/02
Posts: 182
s'what I thought - many thanks