The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
1 registered (sparkyinak), 122 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#40240 - 07/17/04 03:32 AM Romex with cordcap?
shortcircuit Offline
Member

Registered: 06/27/04
Posts: 608
Loc: massachusetts
I have a situation with some romex run up behind one of the new plasma tv mounted on the wall above a fireplace in a family room...the romex is for the 120 volt supply for the tv, but there is not much room for a box and outlet setup, so I wanted to just put a female cord cap on the end of the romex. Is their anything in the code that would prohibit this installation. Also, the other end of the romex runs to the entertainment center where the DVD,VCR,etc are located and I want to terminate that end of the romex with a female 120volt cord cap so we can plug it into a surge protection strip. The piece of romex runs about 10 feet through the wall between where the plasma is and the DVD,VCR,etc are located.Will this be a violation of the code?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#40241 - 07/17/04 04:11 AM Re: Romex with cordcap?
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
Yes it will be a violation.
Cord caps are meant to be used on cord.

Maybe a "clock outlet", (a recessed outlet) is what you're looking for.
It will allow you to plug in a plasma screen, and still have it fit flat on the wall.

Top
#40242 - 07/17/04 04:36 AM Re: Romex with cordcap?
shortcircuit Offline
Member

Registered: 06/27/04
Posts: 608
Loc: massachusetts
electure,thanx for the reply. What article of the code restricts a cord caps use in this way?
Where the TV is set up for installation there is 1/2 blue board over the brick of the fireplace, so we can't recess a box.

Top
#40243 - 07/17/04 06:51 AM Re: Romex with cordcap?
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Shortcircuit UL calls a cord cap an attachment plug.

2002 UL White Book
ATTACHMENT PLUGS, FUSELESS (AXUT)

 Quote:
Attachment Plug — A male contact device for the temporary connection of a flexible cord or cable to a receptacle, cord connector, or other female outlet device.


Notice they specify flexible cord.

They also describe the terminals.

 Quote:
Terminals — Terminals of appliance couplers, appliance and flatiron plugs, attachment plugs, cord connectors and table taps are intended for use with stranded copper conductors of the type used in flexible cord.


And from the NEC

 Quote:
110.3 Examination, Identification, Installation, and Use of Equipment.

(B) Installation and Use.
Listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling.


We can not use equipment in a way that it was not intended to be used.

[This message has been edited by iwire (edited 07-17-2004).]
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#40244 - 07/17/04 07:48 AM Re: Romex with cordcap?
PCBelarge Offline
Member

Registered: 06/08/03
Posts: 657
Loc: Dobbs Ferry, NY, USA
Bob, not to be a pain , I know you had the right idea, but an attachment plug is not a receptacle or cord connector as per UL.
An attachment plug is " a male contact device ...".
a cord connector is " a female contact device to be wired on flexible cord for use as and extension from an outlet to make a detachable electrical connection to an attachment plug or, as an appliance coupler, to a male inlet."

This specifically describes the 'cord connector' as being installed on a flexible cord, and not to a chapter 3 wiring method.

406.6 requires all cord connectors to be listed, that puts us in the direction of the manufacuturer's instructions and the UL White Book.

Pierre
_________________________
Pierre Belarge

Top
#40245 - 07/17/04 09:04 AM Re: Romex with cordcap?
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
I don't usually get males and females mixed up but other than gender (I thought he was using a male on the NM) what I said remains the same.

Attachment plugs and cord connectors are the in the same section of the UL white book.

Bob




[This message has been edited by iwire (edited 07-17-2004).]
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#40246 - 07/17/04 09:28 AM Re: Romex with cordcap?
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA


[This message has been edited by iwire (edited 07-17-2004).]
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#40247 - 07/17/04 10:18 AM Re: Romex with cordcap?
shortcircuit Offline
Member

Registered: 06/27/04
Posts: 608
Loc: massachusetts
thanx...I'll use a shallow wiremould box with a device:< )