The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Yesterday at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 223 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#40030 - 07/10/04 05:33 PM Lighting control panel behind water fountain?
Edward Offline
Member

Registered: 12/14/02
Posts: 309
Loc: California
This is a huge landscape project.
The homeowner will have a waterfall built on a 6'high by 5' wide by 8" thick cementwall.

I am planning to install a 100Amp sub panel for future pool equipment and a landscpae lighting control panel on the backside of the wall. And built an enclosure around the equipment.

I could not find anyhting in the code that prohibits my installation.

Am in any NEC violation?

Regards,
Edward
_________________________
Thanks
Edward

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#40031 - 07/11/04 08:25 AM Re: Lighting control panel behind water fountain?
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
Provided that you will be in compliance with all the working clearances in 110.26, you should have no problem. However, there is a minimum height requirement of 6 1/2 feet, which will be taller than the wall that you're going to mount the equipment on, might be kind of ugly sticking up above the wall.

Seems like the easiest & least expensive thing to do would be to use NEMA 3R enclosures & skip building your own enclosure which would be rather large.

Tom



[This message has been edited by Tom (edited 07-11-2004).]
_________________________
Few things are harder to put up with than the annoyance of a good example.

Top
#40032 - 07/11/04 09:34 PM Re: Lighting control panel behind water fountain?
Big Jim Offline
Member

Registered: 07/18/03
Posts: 377
Loc: Denver, CO USA
Isn't 6' 6" the MAXIMUM height for the main disconnect?

Top
#40033 - 07/12/04 10:01 AM Re: Lighting control panel behind water fountain?
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
Big Jim,

6' 7" is the maximum height of a disconnect switch, as measured to the center of the handle in its highest position 404.8(A)

6' 6" is the minimum headroom in 110.26(E). If Edward builds an enclosure for this equipment, that will be the minimum headroom inside the enclosure. This enclosure is really going to look ugly if he opts to go that route since the inside dimensions will be a minimum of 30" wide & 36" deep(plus the depth of the breaker box). Not to mention that he'll likelyhave to install a light fixture inside.


Tom
_________________________
Few things are harder to put up with than the annoyance of a good example.