The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
International Wire Colour Codes
by Texas_Ranger
Today at 08:24 AM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
230 or 345 kV transmission lines?
by annemarie1
10/12/16 01:23 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
renosteinke 6
HotLine1 6
ghost307 5
Potseal 4
Who's Online
0 registered (), 216 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#40002 - 07/10/04 10:17 AM fire alarm relay for elevator
estman Offline
Junior Member

Registered: 07/06/04
Posts: 3
hello everyone,

I am putting together a fire alarm system.
The panel is an edwards 2414 which is a basic analog one. my question is how I Interface it with the elevator for a recall?

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#40003 - 07/10/04 10:34 AM Re: fire alarm relay for elevator
CRM Offline

Registered: 02/29/04
Posts: 73
Loc: Alberta Canada
The fire alarm panel will have a combination NO/NC alarm contacts. I would use the NO contacts and connect these back to the elevator control panel. The elevator company will show you where to wire into their panel. So when there is an alarm a set of contacts will close, operating the elevator recall at the elevator control panel.

#40004 - 07/10/04 12:51 PM Re: fire alarm relay for elevator

Here's another idea.
I would not recall the elevator on general alarm. I would use a relay type base for the smokes in the elevator lobbies. Wire the relays in parallel so that a fire in any lobby but the main entrance lobby sends the car to first floor (primary) and a fire in the main entrance lobby will send the car to a different floor. (alternate) Also if your shunting the power to the elevator machine room with a heat detector just use a two pole heat using one side for fire alarm and the other side for shunt. Is the building sprinked? It will make a difference on the detection you put in the shaft. You may want to read through NFPA 72 3-9.3 (1999) and a call to the elevator inspector might be worth it. Since, in my area anyway each inspector seems to want it set up a little differently.

#40005 - 07/14/04 12:09 AM Re: fire alarm relay for elevator
estman Offline
Junior Member

Registered: 07/06/04
Posts: 3
thank you guys your answers shed light in my questions.