#39938 - 07/08/04 02:30 PM elect stove wire prob.  
Kennyvp  Offline
Member
Joined: Oct 2003
Posts: 21
New Jersey
a home insp. just caught this on a insp of a property i have. the elect. stove is on a allm 6/2 wire with a 30 amp breaker. the stove requires 40 amps! however he is requiring the wire be changed not just the breaker. he wants 8/3 copper on a 40 amp breaker is this needed or can i just cahnge the breaker/ also can some one tell me the code number for amp ratins on allm wire?


Work Gear for Electricians and the Trades

#39939 - 07/08/04 03:05 PM Re: elect stove wire prob.  
electricman2  Offline
Member
Joined: Nov 2003
Posts: 269
Thomasville, NC USA
6AWG AL has a 60C rating of 40A. I assume you mean type SE cable. If NM is used it will need to be 6/3.


John

#39940 - 07/08/04 04:16 PM Re: elect stove wire prob.  
trekkie76  Offline
Member
Joined: Jun 2004
Posts: 220
baileyville, maine, usa
you would need 8/3 becuase the 6/2 doesn't have a ground. You could get away with 3 wire in an existing intallation, but if you are changing the breaker, you have to bring the circuit up to code. no grounding with the nuetral anymore. 310-16 has ampacities for al.


#39941 - 07/08/04 05:55 PM Re: elect stove wire prob.  
Electricmanscott  Offline
Member
Joined: Jan 2002
Posts: 1,457
Holden, MA USA
How would a breaker replacement require a new circuit be installed? This is not a new installation. If you do change the wire you will not need to use 6/3 for a 40 amp circuit. 8/3 romex will suffice.


#39942 - 07/10/04 06:12 PM Re: elect stove wire prob.  
trekkie76  Offline
Member
Joined: Jun 2004
Posts: 220
baileyville, maine, usa
Maybe it is a local code, but I was always told that if you touch a circuit, you have to bring it up to current code. I can't find it in the NEC, but if it isn't a code rule, I wonder where it came from? anyone else heard of this?



Member Spotlight
NickD
NickD
Amish Country, PA
Posts: 46
Joined: March 2013
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.011s Queries: 14 (0.002s) Memory: 0.7652 MB (Peak: 0.9049 MB) Zlib enabled. Server Time: 2017-03-23 04:11:35 UTC