#39739 - 06/28/04 07:31 PM Conductors in Parallel
Dave55 Offline
Member
Registered: 05/08/04
Posts: 697
Loc: Crystal Lake, Illinois, USA
I have seen 800 amp services using two 500 kcmil conductors for each phase. I'm assuming that the ampacity is figured as 430 amps(THHN) X 2 = 860 amps, rather than as being equivalent to one 1000 kcmil conductor at 615 amps. Would three 250 kcmil parallel conductors be 290 amps X 3 = 870 amps?

Dave
Top
Work Gear for Electricians and the Trades
#39740 - 06/28/04 07:53 PM Re: Conductors in Parallel
Nick Offline
Member
Registered: 08/13/01
Posts: 599
Loc: Riverside, CA
The ampacity is figured using the 75 deg table (380A). Times two conductors is 760A. Then article 240.4 is applied allowing the next higher standard fuse size or 800A.
Top
#39741 - 06/29/04 06:33 AM Re: Conductors in Parallel
earlydean Offline
Member
Registered: 12/22/03
Posts: 751
Loc: Griswold, CT, USA
The 75 degree section is used because of the rating of the termination lugs. See 110.14(C).

Remember also to apply 310.15(B)(2)(a) and derate the conductors if you pull all of the paralled conductors in one conduit.

Earl
_________________________
Earl
Top
#39742 - 06/29/04 09:04 AM Re: Conductors in Parallel
JBD Offline
Member
Registered: 07/12/01
Posts: 599
Loc: WI, USA
The 75C column must be used because UL does not list Overcurrent Protective Devices for use with conductors based on 90C ampacities.
Top
#39743 - 06/29/04 02:24 PM Re: Conductors in Parallel
Tom Offline
Member
Registered: 01/01/01
Posts: 1044
Loc: Shinnston, WV USA
One little detail to watch out for is to be sure that the noncontinuous load plus 125% of the continuous load does not exceed 760 amps for parallel 500kcmil. This is usually not the case since most of us don't cut these things real close to the bone & leave some room for future growth.

Tom
_________________________
Few things are harder to put up with than the annoyance of a good example.
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 74 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals