The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 137 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#39739 - 06/28/04 07:31 PM Conductors in Parallel
Dave55 Offline
Member

Registered: 05/08/04
Posts: 666
Loc: Crystal Lake, Illinois, USA
I have seen 800 amp services using two 500 kcmil conductors for each phase. I'm assuming that the ampacity is figured as 430 amps(THHN) X 2 = 860 amps, rather than as being equivalent to one 1000 kcmil conductor at 615 amps. Would three 250 kcmil parallel conductors be 290 amps X 3 = 870 amps?

Dave

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#39740 - 06/28/04 07:53 PM Re: Conductors in Parallel
Nick Offline
Member

Registered: 08/13/01
Posts: 603
Loc: Riverside, CA
The ampacity is figured using the 75 deg table (380A). Times two conductors is 760A. Then article 240.4 is applied allowing the next higher standard fuse size or 800A.

Top
#39741 - 06/29/04 06:33 AM Re: Conductors in Parallel
earlydean Offline
Member

Registered: 12/22/03
Posts: 749
Loc: Griswold, CT, USA
The 75 degree section is used because of the rating of the termination lugs. See 110.14(C).

Remember also to apply 310.15(B)(2)(a) and derate the conductors if you pull all of the paralled conductors in one conduit.

Earl
_________________________
Earl

Top
#39742 - 06/29/04 09:04 AM Re: Conductors in Parallel
JBD Offline
Member

Registered: 07/12/01
Posts: 599
Loc: WI, USA
The 75C column must be used because UL does not list Overcurrent Protective Devices for use with conductors based on 90C ampacities.

Top
#39743 - 06/29/04 02:24 PM Re: Conductors in Parallel
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
One little detail to watch out for is to be sure that the noncontinuous load plus 125% of the continuous load does not exceed 760 amps for parallel 500kcmil. This is usually not the case since most of us don't cut these things real close to the bone & leave some room for future growth.

Tom