#39542 - 06/24/04 03:49 PM grounding two meter service
richard Offline
Member
Registered: 08/07/03
Posts: 94
Loc: L.I. New York
I installed a two meter service, one feeds a two pole 40, and the other was an upgrade from 100 to 150. I ran a #4 to the water main and used it for the 150 panel. I reused the #6 for the 40 amp panel. I installed two ground rods, one for each panel, seperate from each other. The boss said I was supposed to bond all the grounds together, by running just the #4 from the 150 to the water main, and bug a #6 from the 40 to it, as well as running both ground rod wires to one ground rod. Is there a code that is specific to this situation. (I live on Long Island, Suffolk County, New York. I don't see anything in LIPA"S redbook.
Top
Work Gear for Electricians and the Trades
#39543 - 06/24/04 04:07 PM Re: grounding two meter service
trekkie76 Offline
Member
Registered: 06/19/04
Posts: 220
Loc: baileyville, maine, usa
in 250-50, if available on the premises, each item 1-6, shall be bonded together to form the grounding electrode system.
1. metal underground water pipe
2.metal frame of a building
3.concrete encased electrode
4.ground ring
5.rod or made electrode
6.plate electrodes
Top
#39544 - 06/25/04 04:20 AM Re: grounding two meter service
velect Offline
Member
Registered: 05/01/04
Posts: 81
Loc: st joseph mi usa
I did a similar service

I ran #6 from one panel to the other and then out to two ground rods 6 foot apart. One continuous ground going right through one of the neutral bar lug and through both clamps on the groumd rods. Then took a #4 bond wire and bonded the water and gas system out of one of the panels.

Passed with no problems
Top
#39545 - 06/25/04 11:55 AM Re: grounding two meter service
SJT Offline
Member
Registered: 07/24/02
Posts: 241
Loc: PATCHOGUE, N.Y.
What size is the service conductors that feed the 2 gang meter (double meter). You base the size of the ground wire back to the water pipe on 250.66. From that, I would bug off to each panel, and not jump from one Bus to the other.
Top
#39546 - 06/25/04 04:34 PM Re: grounding two meter service
Admin Online   content

Administrator
Member
Registered: 10/07/00
Posts: 3417
Loc: NY, USA
Quote:
I guess I didn't look hard enough in the redbook.

- richard
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6775
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 14 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals