The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by ghost307
Today at 06:25 AM
International Wire Colour Codes
by Tjia1981
Yesterday at 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 288 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#39542 - 06/24/04 03:49 PM grounding two meter service
richard Offline

Registered: 08/07/03
Posts: 84
Loc: L.I. New York
I installed a two meter service, one feeds a two pole 40, and the other was an upgrade from 100 to 150. I ran a #4 to the water main and used it for the 150 panel. I reused the #6 for the 40 amp panel. I installed two ground rods, one for each panel, seperate from each other. The boss said I was supposed to bond all the grounds together, by running just the #4 from the 150 to the water main, and bug a #6 from the 40 to it, as well as running both ground rod wires to one ground rod. Is there a code that is specific to this situation. (I live on Long Island, Suffolk County, New York. I don't see anything in LIPA"S redbook.

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#39543 - 06/24/04 04:07 PM Re: grounding two meter service
trekkie76 Offline

Registered: 06/19/04
Posts: 219
Loc: baileyville, maine, usa
in 250-50, if available on the premises, each item 1-6, shall be bonded together to form the grounding electrode system.
1. metal underground water pipe
2.metal frame of a building
3.concrete encased electrode
4.ground ring
5.rod or made electrode
6.plate electrodes

#39544 - 06/25/04 04:20 AM Re: grounding two meter service
velect Offline

Registered: 05/01/04
Posts: 79
Loc: st joseph mi usa
I did a similar service

I ran #6 from one panel to the other and then out to two ground rods 6 foot apart. One continuous ground going right through one of the neutral bar lug and through both clamps on the groumd rods. Then took a #4 bond wire and bonded the water and gas system out of one of the panels.

Passed with no problems

#39545 - 06/25/04 11:55 AM Re: grounding two meter service
SJT Offline

Registered: 07/24/02
Posts: 242
What size is the service conductors that feed the 2 gang meter (double meter). You base the size of the ground wire back to the water pipe on 250.66. From that, I would bug off to each panel, and not jump from one Bus to the other.

#39546 - 06/25/04 04:34 PM Re: grounding two meter service
Webmaster Offline


Registered: 10/07/00
Posts: 3142
Loc: NY, USA
I guess I didn't look hard enough in the redbook.

- richard