#39539 - 06/24/04 02:48 PM service bonding
trekkie76 Offline
Member
Registered: 06/19/04
Posts: 220
Loc: baileyville, maine, usa
hello all, I have a question about bonding. I have an existing 120/208 3ph service, 400 amps in a bank. we are there to fix code voilations so the local inspector can sign off before the new occupants can come in. the problem is there are 5 panels fed from an aux. gutter, and no bonding bushings. There are insulating bushings, and all of the conduit is ridgid or emt, my question is can I bond the conduits outside the aux. gutter, just clamp to each pipe? I just don't want to tear into the taps!! Any advice would be appreciated.
Top
Work Gear for Electricians and the Trades
#39540 - 06/24/04 04:08 PM Re: service bonding
electricman2 Offline
Member
Registered: 11/09/03
Posts: 269
Loc: Thomasville, NC USA
Tomas & Betts makes a grounding wedge for this use. Here is the link. .It is available in 1/2 to 6 inch.
_________________________
John
Top
#39541 - 06/24/04 04:18 PM Re: service bonding
trekkie76 Offline
Member
Registered: 06/19/04
Posts: 220
Loc: baileyville, maine, usa
those things are exactly what I need!! thanks for the link!!
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 54 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals