The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Yesterday at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 203 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#39402 - 06/18/04 06:26 PM Sub in Garage
Zapped Offline
Member

Registered: 10/01/02
Posts: 481
Loc: Huntington Beach, CA, USA
Any code problems with putting an 125A sub panel in a garage? If so, could somebody site the section please?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#39403 - 06/18/04 06:29 PM Re: Sub in Garage
Electric Eagle Offline
Member

Registered: 04/20/02
Posts: 928
Loc: Alpharetta, GA
Not a problem at all. If the garage is a detached building, it needs its own grounding system.

Top
#39404 - 06/18/04 06:41 PM Re: Sub in Garage
caselec Offline
Member

Registered: 04/14/02
Posts: 557
Loc: San Jose, CA
If its an attached garage don't put it in the firewall.
_________________________
Curt Swartz

Top
#39405 - 06/18/04 08:07 PM Re: Sub in Garage
techgod Offline
Member

Registered: 12/15/03
Posts: 20
Loc: Burbank, Ca USA
If it is a detached garage it needs its own main breaker/disconnect 225.30 (Some AHJ's require this be on the exterior), and a EGC going back to the main house panel in addition to the grounding system at the garage. 250.32(A)

Mark Stetson
_________________________
Mark Stetson
Stetson Electric

Top
#39406 - 06/18/04 10:39 PM Re: Sub in Garage
Zapped Offline
Member

Registered: 10/01/02
Posts: 481
Loc: Huntington Beach, CA, USA
Thanks for the rapid replies. The garage is attached, and my proposed location for the sub is on the wall between the garage and the interior of the house. Is this going to be a problem?

Thanks again!

Top
#39407 - 06/19/04 01:51 AM Re: Sub in Garage
e57 Offline
Member

Registered: 05/27/03
Posts: 2837
Loc: S.F.,CA USA
Check for the fire wall rating, some local codes will require a 1, or 2 hour rating for a wall from a garage to dwelling space. Condo's especially! So in this case your openings would need to be of a certain (small TBA) size. Depanding on the fire code. Or you'll have to go with a surface panel. In some cases like this I'll have the general put up the rock where the panel will be, put a 14x14x4 box above it, stub all the cable evenly in a pattern into the back of it. (2 for larger circuit counts) Then a 2 1/2" nipple into the panel. This way, it's a pattern of small holes, (that you can feed and chalk from the back) as opposed to a 14x36" hole. Theres nothing sillier than a rock box, and chaulk for a panel!

I put cans in cieling that i didn't know was going to be fire rated once, boy was that a mistake!
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason

Top
#39408 - 06/21/04 02:22 PM Re: Sub in Garage
triple Offline
Member

Registered: 04/01/02
Posts: 182
Loc: Wisconsin
Techgod, a separate EGC is not needed from the house to a detached garage as long as there are no other metallic connections between the two buildings (TV, phone, water pipe, etc...). However, I personally would never run only three wire for a detached garage (I doubt that any licensed/informed electrician would).

Top