ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

ECN Shout Chat
Top Posters(30 Days)
Admin 19
Recent Posts
Anyone hiring inspectors?
by HotLine1. 03/27/17 08:03 AM
Old decora style outlets
by Admin. 03/25/17 11:40 AM
ESA Arc flash course
by TheShockDoctors. 03/24/17 10:15 AM
fuse rejectors
by HotLine1. 03/24/17 07:53 AM
Another Forum Update
by Admin. 03/22/17 03:04 PM
New in the Gallery:
SE cable question
Popular Topics(Views)
231,651 Are you busy
166,552 Re: Forum
160,731 Need opinion
Who's Online Now
0 registered members (), 84 guests, and 8 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#39090 - 06/08/04 10:11 PM Isolated ground runs.  
Sandro  Offline
Member
Joined: Dec 2001
Posts: 444
Stoney Creek, ON, Canada
Do I need to run a separate ground from the panel to EACH isolated ground receptacle, or can I run a single insulated ground conductor from the panel and stop off at each junction box and pick up each IGR at each station JB? Is there a limit to how many IG I can pick off of a single line?


Work Gear for Electricians and the Trades

#39091 - 06/08/04 11:14 PM Re: Isolated ground runs.  
twh  Offline
Member
Joined: Mar 2004
Posts: 903
Regina, Sask.
In Canada, see rule 10-906(9)


#39092 - 06/09/04 03:26 AM Re: Isolated ground runs.  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
It is up to you and the job specifications.


Bob Badger
Construction & Maintenance Electrician
Massachusetts

#39093 - 06/09/04 05:10 PM Re: Isolated ground runs.  
Radar  Offline
Member
Joined: Apr 2004
Posts: 349
Los Angeles, CA
IG doesn't mean dedicated ground for each outlet. As Iwire says, check your specifications. Generally it means a separate isolated and insulated grounding wire besides the equipment grounding conductor.

So, for a 120V outlet, one would end up with a hot, a neutral, an equipment ground (for the conduit & outlet box), and an isolated ground (for the ground prong of a receptacle).

You can usually string several IG outlets together without a problem, depending on specifications. However, some engineers and/or specifiers have different ideas about what IG means.

Lastly, if the breaker panel feeding your circuit does not have an IG bus with an upstream isolated ground conductor back to the main, are you really getting an isloated ground?

Radar


There are 10 types of people. Those who know binary, and those who don't.


Member Spotlight
RH1
RH1
California
Posts: 22
Joined: August 2009
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.013s Queries: 14 (0.003s) Memory: 0.7582 MB (Peak: 0.8889 MB) Zlib enabled. Server Time: 2017-03-28 19:44:31 UTC