The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
International Wire Colour Codes
by Texas_Ranger
Today at 03:29 PM
Looking for older post
by Texas_Ranger
Today at 03:22 PM
Safety at heights?
by gfretwell
Today at 02:19 AM
Last time to chat here
by Trumpy
Yesterday at 11:41 PM
Unsafe Situations
by Trumpy
Yesterday at 09:46 PM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
Admin 35
HotLine1 20
Trumpy 19
Ruben Rocha 17
gfretwell 16
Who's Online
0 registered (), 67 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#38947 - 06/06/04 04:28 PM Sub panel
oc-nj 08757 Offline
Member

Registered: 06/04/04
Posts: 13
Loc: Manchester Twp. NJ
I have someone who wants me to put a 100amp sub panel in their basement. There is already a piece of number 2 SEU running from the main panel to where he wants the sub panel which is not being used for anything. Is there anything I can do to get an additional conductor over or do I need to rip out the SEU and replace it with SER? Any ideas would be appriciated...

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#38948 - 06/06/04 06:17 PM Re: Sub panel
PCBelarge Offline
Member

Registered: 06/08/03
Posts: 657
Loc: Dobbs Ferry, NY, USA
You do not need to rip out the SE, but you will need 4 conductors to the subpanel, 2 ungrounded, one grounded, and one equipment grounding conductor. All of them installed in the same raceway or cable.

Pierre
_________________________
Pierre Belarge

Top
#38949 - 06/06/04 08:20 PM Re: Sub panel
Attic Rat Offline
Member

Registered: 12/14/03
Posts: 530
Loc: Bergen Co.,N.J. USA
... You NEED to run SER,...it has 2 phase conductors,a neutral,and a ground...anything less than this is a Code violation..also, DO NOT bond the sub-panel's green ground screw to the enclosure..a separate grounding bar is needed here..
Russ
_________________________
.."if it ain't fixed,don't break it...call a Licensed Electrician"

Top
#38950 - 06/07/04 02:27 PM Re: Sub panel
oc-nj 08757 Offline
Member

Registered: 06/04/04
Posts: 13
Loc: Manchester Twp. NJ
Thanks for the reply's. I've done a ton of these, but I was hopeing to save some $$$ on the wire by finding a legal way to run only 1 conducter instead of buying the SER since there is already a piece of SEU going to where I want to be.