The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 88 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#38781 - 06/01/04 09:28 PM Electric Current in Gas Pipes?
ThinkGood Offline

Registered: 08/07/02
Posts: 1084
Loc: Milwaukee, WI
From an insert included with the latest gas/electric bill:


Keep Metal Objects Away From Your Gas Meter

It is important to keep metal away from your gas meter. PSE&G uses metal pipes that are protected from corrosion by a small electrical current running through them. This makes the pipes stronger and more efficient. If attached to these pipes, metal objects (such as a dog's leash or an antenna) strip the corrosion protection and cause problems with the electricity running through the pipes. When pipes become damaged, they may not work as well, and we may need to fix them.

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#38782 - 06/01/04 09:51 PM Re: Electric Current in Gas Pipes?
frenchelectrican Offline


Registered: 02/06/03
Posts: 938
Loc: Wi/ Paris France { France for ...

i dont know what to say but that is very odd but i did heard some kind of protection by injecting small DC not AC current with very low votage too.

myself i did see one on major petroleum pipeline it have small power device to inject the dc power to prevent corrosion on pipe line.

i know this is kinda of odd item to see it but if anyone else know about this please do pitch in here.

merci, marc
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)

#38783 - 06/01/04 10:25 PM Re: Electric Current in Gas Pipes?
nesparky Offline

Registered: 06/21/01
Posts: 650
Loc: omaha,ne
This is called cathodic protection. It is a way of preventing corrosion on metals. It is a specilized circuit that some where has a sacrifical metal that is supposed to corrod (rust away) before the metal bieng protected.
It's an intersting subject, but expensive to install and requires regular testing.

#38784 - 06/01/04 11:28 PM Re: Electric Current in Gas Pipes?
Lostazhell Offline

Registered: 02/21/04
Posts: 1248
Loc: Bakersfield, CA (Originally Or...
Ahhh... This reminds me of something... A few AHJ's out here want gas to be bonded back to the panel, along with the normal things... I have (had... I gotta look for it again,) a formal letter from So Cal Gas Co. stating they DO NOT want their system bonded to the electrical grounding system... I get fun looks when I pull this out during inspections! A couple places want it anyways... Could this have something to do with that?? I always thought it was better if a hot wire hit a gas line that it didn't spark!


#38785 - 06/02/04 03:09 AM Re: Electric Current in Gas Pipes?
iwire Offline

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Randy while the NEC does not allow gas lines as a grounding electrode the NEC requires the gas piping in the house to be bonded. Around here gas lines are threaded or welded black iron pipe.

So in the structure the gas lines are bonded.

I imagine they install a dielectric coupling at the meter in order to provide the cathodic protection.

250.104(B) Other Metal Piping. Where installed in or attached to a building or structure, metal piping system(s), including gas piping, that may become energized shall be bonded to the service equipment enclosure, the grounded conductor at the service, the grounding electrode conductor where of sufficient size, or to the one or more grounding electrodes used. The bonding jumper(s) shall be sized in accordance with 250.122 using the rating of the circuit that may energize the piping system(s). The equipment grounding conductor for the circuit that may energize the piping shall be permitted to serve as the bonding means. The points of attachment of the bonding jumper(s) shall be accessible.

Unless you are installing dielectric fittings on the gas line at the hot water heater the gas line ends up bonded anyway.
Bob Badger
Construction & Maintenance Electrician

#38786 - 06/02/04 03:59 AM Re: Electric Current in Gas Pipes?
winnie Offline

Registered: 09/15/03
Posts: 652
Loc: boston, ma
This goes to different authorities with different (and conflicting) requirements. Metal piping systems in the house should be bonded, both IMHO and by NEC. But plumbers hate underground water pipe as the grounding electrode, the NEC prohibits the use of underground gas pipe as a grounding electrode, and clearly the gas company doesn't like it either.

IMHO the 'best' way to balance all of this is to have dielectric couplings in any underground metal piping systems where they enter structures, to bond this piping internally, but to explicitly not use this piping as a grounding electrode. This would help eliminate the problems of neutral currents flowing on metal piping, something that happens in urban areas where houses that use the same water pipes all bond them to neutral in their main panels; net result is multiple bonds between neutral and a continuous metallic system, and thus significant parallel paths.

This would require a change in the NEC, since an underground water pipe of sufficient length is _required_ to be used as a grounding electrode.


#38787 - 06/02/04 04:17 AM Re: Electric Current in Gas Pipes?
ThinkGood Offline

Registered: 08/07/02
Posts: 1084
Loc: Milwaukee, WI
OK, a dielectric at the meter makes sense. However, the pipe that enters the meter is coming from under the ground.

How do they keep the electric current on the pipe if it's in contact with the ground? I know for certain that under the street the pipe is in direct contact with the earth, based on some emergency digging once done around here.

Maybe this should be moved to theory...can somebody explain the cathodic protection in terms of how the current doesn't just go to ground?


#38788 - 06/02/04 05:35 AM Re: Electric Current in Gas Pipes?
C-H Offline


Registered: 09/17/02
Posts: 1508
Loc: Stockholm, Sweden
Isn't the whole point that the current goes to ground? (Low voltage = not much current)

I like Winnies idea!

#38789 - 06/02/04 09:17 AM Re: Electric Current in Gas Pipes?
Mean Gene Offline

Registered: 10/20/03
Posts: 137
Loc: Ohio, USA
A very interesting topic. In my area, everyone gets flexible plastic pipe, yellow in color, with a stranded yellow tracer wire of about 8 gauge from the main to the building. The wire isn't connected to anything. It's just there to aid in locating the pipe underground.

#38790 - 06/02/04 01:15 PM Re: Electric Current in Gas Pipes?
hbiss Offline

Registered: 12/16/03
Posts: 893
Loc: Hawthorne, NY USA
Around here all new and recent gas services are poly pipe. AND I have noticed rectifiers in cabinets mounted on poles apparently for cathodic protection but this seems to be for the larger distribution lines. Don't know if it would still energize the smaller mains.