The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Potseal 6
Who's Online
0 registered (), 92 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#38618 - 05/27/04 07:28 PM 2,3 pole breakers
seattleman Offline
Member

Registered: 02/01/04
Posts: 17
Loc: Seattle, WA, USA
when a breaker is listed as 2,3pole on a 277, 480 panel, this means it can be used as overcurrent protection of a 3phase 3wire 480 load or a 1 phase 2 wire 277 load (never done this, but make sence to me.

If you only use to hole of a three wire breaker does it matter which two hole you use? I thinking about the balancing of all three phases in the panel. -thanks

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#38619 - 05/27/04 07:37 PM Re: 2,3 pole breakers
Ryan_J Offline
Moderator

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
Doesn't matter in your scenario. 240.85 comes into play on non-solidy grounded systems though, such as high-impedance grounded, corner grounded, mid point phase grounded and ungrounded.