The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by HotLine1
Today at 01:42 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
Texas_Ranger 8
sparkyinak 8
Potseal 6
Who's Online
2 registered (Webmaster, LongRunner), 227 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#38371 - 05/21/04 07:02 AM Transformer Fuses for Commercial 3PH
Dave55 Offline
Member

Registered: 05/08/04
Posts: 666
Loc: Crystal Lake, Illinois, USA
I have a question for any line-workers (U.S.A.).

I'm installing 800A Delta 120/208/240 3PH services and was wondering about the size of the transformer fuses. I use gear with an 800A breaker. In another thread is a discussion about fuses and breakers.

My curiosity is this...if there were a short in this service and it flashed, the fuse at the transformer might be more reliable in disconnecting than the main breaker, so why have a main breaker? There will be six or less disconnects in this service (usually 4 or 5).

There are two pole-mounted transformers for each of these 800A services.

Another question I have is...does anyone have a wiring diagram for how they get 3PH from two HV wires. I've seen winding diagrams for Delta secondaries, but not for the primary with the secondary.

Any help or comments would be greatly appreciated.

Dave

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#38372 - 05/21/04 11:37 AM Re: Transformer Fuses for Commercial 3PH
Bjarney Offline
Moderator

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
Who owns the transfomers? Are you saying there are two 1ø 120/240V-secondary transformers serving an 800A service?

Top
#38373 - 05/21/04 06:32 PM Re: Transformer Fuses for Commercial 3PH
Dave55 Offline
Member

Registered: 05/08/04
Posts: 666
Loc: Crystal Lake, Illinois, USA
I feel like an idiot about this, but there are two things hanging on the pole, one larger than the other. They are owned by the POCO.

Top
#38374 - 05/21/04 07:08 PM Re: Transformer Fuses for Commercial 3PH
Bjarney Offline
Moderator

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
Distribution-transformer installations in the US are generally designed under ANSI C57 standards, with engineering review adjusted for regional practices and local adaptations. There a thousands of electric utilities on the North American continent, and few are the same when it comes to distribution construction and operating practices.

Top
#38375 - 05/21/04 07:57 PM Re: Transformer Fuses for Commercial 3PH
Bjarney Offline
Moderator

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
One very general distribution-transfomer configuration reference is www.cooperpower.com/Library/pdf/R201902.pdf It sounds like you may be describing an open-wye-primary, open-delta-secondary bank similar to figure 21.

If the two 1ø transfomers are not of equal kVA ratings, it is because the utility intends for the lighting/general 1ø 3-wire loads directly connected to the larger transfomer via lo-side “bø” and “cø.” Additional 3ø 3-wire loads like motors are fed from both 1ø transformers. In figure 21, the transformer with X2 unconnected is typically the smaller transfomer. {The non-symmetrical bank is anticipated for intentionally unbalanced secondary-phase currents.} In figure 21, lo-side “aø” is connected only to 3ø loads [that are also served from lo-side “bø” and “cø.”] Lo-side “aø” in the diagram is also called the “stinger”/”wild”/”power” leg. [It is more common for US utilities to designate lo-side bø (or cø) as the high leg.]

It is normal for an open-delta-secondary bank to experience some ø-ø voltage unbalance on the loaded transfomer bank, but is typically limited to no more than 5%. In the usual 3-wire delta and 3- or 4-wire wye systems where all transfomeres are sized equally, phase currents are best equally balanced.

www.cooperpower.com/library/pdf/02022.pdf and, www.cooperpower.com/library/pdf/R240306.pdf on basic distribution-transformer fuse data.




[This message has been edited by Bjarney (edited 05-21-2004).]

Top
#38376 - 05/22/04 04:16 AM Re: Transformer Fuses for Commercial 3PH
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
Great post Bjarney!.
Us guys over here had the 2 transformers up on a set of poles + a platform for the Xformers.
Purely 22kV Line stabilisation, but as far as I know they were configured in a Scott Connection, where 2 HV windings feed 3 HV windings of the same voltage.
Can you shed some light on this Bjarney?.
Not long before I left Temuka, to come to Ashburton, they were Undergrounding all the services and the Scott Connection was lost, in that part of the world.
Changed for plain vanilla Delta-Star Xformers.
Damn, take all the fun out of life why don't they!.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#38377 - 05/22/04 07:27 AM Re: Transformer Fuses for Commercial 3PH
Dave55 Offline
Member

Registered: 05/08/04
Posts: 666
Loc: Crystal Lake, Illinois, USA
Thanks, Bjarney. This is exactly what I was looking for!

Dave

Top
#38378 - 05/22/04 10:21 AM Re: Transformer Fuses for Commercial 3PH
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
Thanks, Bjarney!!
Those are some very informative links.
(You sure can find 'em)...S

Top
#38379 - 05/22/04 12:57 PM Re: Transformer Fuses for Commercial 3PH
Bjarney Offline
Moderator

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
Variations of Scott(-Tee) connections are covered in the Cooper R201902 bulletin in figures 25+.

More importantly — Although it’s slowly getting better in some respects, relying on the web for information can have its perils. Be very careful about making decisions that affect your own and others’ safety where information is web-based. Do not forget it may be worth exactly what you paid for it—or a lot worse—it may have very serious costs. Providers of “free” information don’t always have your best interests in mind. In the longer run, you may have to critically question their motives for providing “free” stuff. Web information is almost always terse and can be notoriously incomplete or incorrect.

Free advice from anonymous sources can be a very dangerous way of doing business.

Top
#38380 - 05/24/04 07:25 AM Re: Transformer Fuses for Commercial 3PH
JBD Offline
Member

Registered: 07/12/01
Posts: 599
Loc: WI, USA
Three phase T-connections are created by using two transformers with center taps on the primary and secondary windings. The "teaser" transformer is connected to the center tap of the "main" transformer. If the transformers have 10% taps available the output voltage can be made much more symmetrical than a standard open-delta configuration. Most dual voltage transformers can be connected in a T arrangement.

The Scott connection is a modified T connection which uses a standard center tapped "main" transformer and a special "teaser" transformer with a tap at 86.6% instead of at the center. This special tap location provides a "neutral" connection for a 3-phase 4-wire output. Most commercially built three phase transformers smaller than 15KVA are built using arrangement. Another common use is for creating a true 2-phase system from an existing 3-phase grid.