#37690 - 05/04/04 08:46 PM Service Relocation
Attic Rat Offline
Member
Registered: 12/14/03
Posts: 524
Loc: Bergen Co.,N.J. USA
... I'm starting a good job,where the H.O. wants me to move the service to the other side of the house..(had to ask the PoCo inspector,..but he said it's OK)as well as upgrade to 200amps..AND wire the newly installed central A/C system..At first,I was gonna bus all the existing home-runs to the new panel location,...then I had an "Epiphany"...or a moment of "clarity"..Why can't I just install a main-lug panel,run 100 amp.SER, and use it as a sub-panel..Sounds easier,and cheaper than running all the home-runs over to the new panel...Does this make sense..??
Russ
_________________________
.."if it ain't fixed,don't break it...call a Licensed Electrician"
Top
Work Gear for Electricians and the Trades
#37691 - 05/04/04 10:46 PM Re: Service Relocation
Lostazhell Offline
Member
Registered: 02/21/04
Posts: 1428
Loc: Bakersfield, CA (Originally Or...
Done all the time out here Russ..... Typically a "blank" will be out in the old meter socket.. Backfeed the bus with a breaker of proper rating for the panel & the feeders you will use & reconnect to a breaker at the new service..

-Randy
Top
#37692 - 05/05/04 02:26 PM Re: Service Relocation
Megawatt Offline
Member
Registered: 03/11/04
Posts: 76
Loc: Lexington,Ky, USA
With that distance, it's the best option.
Good Idea !
Top
#37693 - 05/05/04 04:13 PM Re: Service Relocation
kody wilson Offline
Member
Registered: 03/17/04
Posts: 11
Loc: vancouver wa. 98664
you will still need a main breaker in the sub panel enless the main panel is in sight of it.
Top
#37694 - 05/05/04 04:31 PM Re: Service Relocation
hbiss Offline
Member
Registered: 12/16/03
Posts: 886
Loc: Hawthorne, NY USA
you will still need a main breaker in the sub panel enless the main panel is in sight of it.

You do? Where does it say that?

-Hal
_________________________
www.myphonetechs.com
Top
#37695 - 05/05/04 04:40 PM Re: Service Relocation
Electricmanscott Offline
Member
Registered: 01/12/02
Posts: 1457
Loc: Holden, MA USA
Sounds like a good idea provided existing panel is worth saving. You probably already know that you won't need a main breaker in the sub panel. What table will you use to size the feeder?
Top
#37696 - 05/05/04 07:46 PM Re: Service Relocation
kody wilson Offline
Member
Registered: 03/17/04
Posts: 11
Loc: vancouver wa. 98664
Article 230 chapter seven {230.91}

"The service overcurrent device shall be an integral part of the service disconnecting means or shall be located immediately adjacent thereto."
But we are talking about {feeders} to the sub panel.
I'm just thinking the sub. still needs a disconect right? because the main isn't with in sight and 50'.
Top
#37697 - 05/05/04 07:49 PM Re: Service Relocation
kody wilson Offline
Member
Registered: 03/17/04
Posts: 11
Loc: vancouver wa. 98664
use table 310.15 {b}{6} for sizeing.
Top
#37698 - 05/09/04 07:17 PM Re: Service Relocation
triple Offline
Member
Registered: 04/01/02
Posts: 184
Loc: Wisconsin
Kody, look up the code definition of a "service" and you will see why the article you referenced does not apply to the subpanel in the case discussed.

…and I’m not even going to get into 310.15(B)(6). If the code making panel is going to do such a half-azzed job of explaining its position, then we as electricians should not be expected to read their collective mind.
Top
#37699 - 05/09/04 07:55 PM Re: Service Relocation
PCBelarge Offline
Member
Registered: 06/08/03
Posts: 681
Loc: Dobbs Ferry, NY, USA
I agree with Triple, and as for 310.15(B)(6), that is not for the panels past the service equipment. Size the conductors from 310.16 (table).
The definition of service is in Art 100.

Pierre
_________________________
Pierre Belarge
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 01/22/05
Posts: 5316
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 54 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals