The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Correct rotation, wrong sequence
by Potseal
Today at 03:14 PM
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 12
HotLine1 10
Potseal 9
sparkyinak 8
Texas_Ranger 7
Who's Online
1 registered (cableguy619), 212 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#37648 - 05/01/04 01:08 PM fire dampers
seattleman Offline
Member

Registered: 02/01/04
Posts: 17
Loc: Seattle, WA, USA
I have a question about the wiring of fire damper motors used to cut off movement of air between rooms and hallways in case of fire.

How do they interact with fire alarm cable. I assume the power feed is probably #12 wire or mc cable to a switch located near the damper and then the switch leg goes to feed the little motor.

But where does this power come from and how does it communicate with the fire alarm control panel? -thanks

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#37649 - 05/01/04 02:53 PM Re: fire dampers
techgod Offline
Member

Registered: 12/15/03
Posts: 20
Loc: Burbank, Ca USA
Fire Dampers usually run on 120V dedicated circuits.

Typically there is a heat or smoke detector on one or both sides of the fire wall mounted on a relay base or with internal relays.

Most of the dampers I've installed require power to close but have a fusible link usually around 185F in case the power is out.

The detectors are wired into the Fire Alarm Panel plus they have the additional contacts for the damper to operate. If one of these detectors goes into alarm the damper will close and the FA panel go into alarm unless you are in an older building with dampers but no Fire Alarm.
_________________________
Mark Stetson
Stetson Electric

Top
#37650 - 05/01/04 09:08 PM Re: fire dampers
DougW Offline
Member

Registered: 06/08/03
Posts: 1083
Loc: North Chicago, IL
They can be shut by system activation, or zone activation. Zone activation is what you're describing - the system in the rest of the building stays in "normal" mode, but if there's a detector off on the 2nd floor, then the 2nd floor HVAC gets isolated.
General activation (not sure if that's the "proper" term) shuts down the HVAC in case the fire alarm goes off, and doesn't turn back on until the system resets, or FD activates it (see below).

We've also seen them tied into duct detectors - smoke in the duct shuts down the system, and the dampers. When the FD resets, system goes back to normal. Usually the duct dectector is wired to an LED on the outside of the duct, or in the adjoining passageway, to assist in locating the detector.

Fancier systems also have an "FD" override, for evacuation of nuisance smoke - basically, it's a preset where the fans will turn on, and certain dampers will open to exhaust fumes / smopke from an area, but only if the FD / building security activates that aspect of the system.

Top
#37651 - 05/02/04 01:13 PM Re: fire dampers
kody wilson Offline
Member

Registered: 03/17/04
Posts: 13
Loc: vancouver wa. 98664
the FSD's that Ive seen open on power and close on loss of power. Due to the wound up spring. close upon power loss seems to make more sence. If heat or fire was to trip breakers or damage a cable before the fsd closed.

Top
#37652 - 05/03/04 09:27 PM Re: fire dampers
gary long Offline
Member

Registered: 02/20/01
Posts: 33
Loc: Greeley,Colorado,USA
I have always put them on the door holder circuit on many buildings in Seattle.

Top
#37653 - 05/06/04 08:02 AM Re: fire dampers
badgers Offline
Junior Member

Registered: 05/09/03
Posts: 8
Loc: madison
does your building have a smoke evacuation system? If so, Relay bases on local detectors may not be enough.

If you have a generator I would use a 120V equipment branch circuit.

I have never used a Smoke damper that required power to close. I have seen units that close whenever power is droped. If it is a Fire/Smoke damper it will have a fusible link that will drop the damper. I have always used a Macabe link. This will drop the damper 'independantly' of the fire alarm system. The ones I have used mechanically break the linkage from the motor. Because the ones I use Spring closed(not powered closed) the damper snaps shut, regardless if the fire alarm wiring is intact, or if power is on.

Top
#37654 - 05/06/04 09:48 AM Re: fire dampers
GETELECTRIC Offline
Member

Registered: 10/22/03
Posts: 178
Loc: toronto canada
you can use a double voltage relay in order to accomplish this as well.