#36614 - 04/10/04 10:14 AM Pool light, separate circuit?
aldav53 Offline
Member
Registered: 08/22/01
Posts: 547
Loc: Chandler, AZ USA
Residential swimming pools usually have their own separate circuit running to a GFI recept, through a switch, and then to the pool light. Does it have to be a separate circuit or can I install a new run by tapping to another exhisting circuit to run the pool lights. (Providing the exhisting circuit is not loaded up too much).
This is a repair.
_________________________
The Golden Rule - "The man with the gold makes the rule"
Top
Work Gear for Electricians and the Trades
#36615 - 04/10/04 09:51 PM Re: Pool light, separate circuit?
aldav53 Offline
Member
Registered: 08/22/01
Posts: 547
Loc: Chandler, AZ USA
Also, there are 2 lights on this pool.
_________________________
The Golden Rule - "The man with the gold makes the rule"
Top
#36616 - 04/11/04 02:11 AM Re: Pool light, separate circuit?
rizer Offline
Member
Registered: 01/03/04
Posts: 90
Loc: bradenton ,fl.,usa
when you say its fed from a "gfci and through a switch" does it have a step down xfmr? Is this an existing pool light where your adding another light? Is there a panelboard at the site of the pool equipment(if any)? You should definetly see article 680 of the NEC. At present, more information about the conditions are needed. Pool lighting is dangerous business if not installed correctly. If this is a side job you might want to consider passing on it.
Top
#36617 - 04/11/04 09:41 AM Re: Pool light, separate circuit?
aldav53 Offline
Member
Registered: 08/22/01
Posts: 547
Loc: Chandler, AZ USA
Yes, it is an exhisting pool light,
(2 lights) and has a panelboard at the filter where the 1 circuit for the GFI recept for the lights are fed from, (but rusted out and broke underground). It does not need a transformer, they are 120v pool lights.
If I were to tap a circuit for the pool lights, it would be a much shorter run than from the panel. But I may need to do that.
_________________________
The Golden Rule - "The man with the gold makes the rule"
Top
#36618 - 04/11/04 02:46 PM Re: Pool light, separate circuit?
rizer Offline
Member
Registered: 01/03/04
Posts: 90
Loc: bradenton ,fl.,usa
680-6(b)lighting fixtures etc
(2)existing lighting fixtures and lighting outlets located less than 5 ft measured horoizontaly from the inside walls of a pool shall be at least 5 ft above the surface of the maximum water level, shall be rigidly attached to the existing structure, and shall be protected by a groundfault circuit interupter.
(c)switching devices. switching devices on the property shall be located at least 5 ft horizontally from the inside walls of a pool unless separated from the pool by a solid fence, wall, or other permanent barrier.
680-10. underground wiring location. underground wiring shall not be permitted under the pool or within the area extending 5ft horizontally from the inside wall of the pool.

this is only a sampling of the code. it seems that you could use another source other than the panel but there is yet another code in this section which requires no less than a #12 ground wire.
do you have access to a code book? if not i would check with your local library. swiming pools are extremely dangerous places with regards to electricity.
Top
#36619 - 04/12/04 07:58 PM Re: Pool light, separate circuit?
aldav53 Offline
Member
Registered: 08/22/01
Posts: 547
Loc: Chandler, AZ USA
I looked through the code book and couldn't find anything on having to put a pool light on a separate circuit.
_________________________
The Golden Rule - "The man with the gold makes the rule"
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM
Looking for older post
by Texas_Ranger
01/21/17 03:22 PM
Last time to chat here
by Trumpy
01/20/17 11:41 PM

Who's Online
1 registered (Admin), 86 Guests and 17 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 10/07/00
Posts: 3188

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals