Is it OK to mount the disconnect on the rooftop unit? I think it is a bad idea, even if permissible. But, there is no existing mounting rack on the roof, and fabricating one would mean securing it to the roof, which would potentially cause leaks in the future.

Thanks,

John
Top
Work Gear for Electricians and the Trades
#36499 - 04/08/04 06:07 AM Re: Rooftop unit follow-up
Bomzin Offline
Member
Registered: 03/25/04
Posts: 27
Loc: Utah
Yes it's ok, usually mounted right on the unit itself. Why would it be a bad idea, worse idea not to have one.

Bomzin
Top
#36500 - 04/08/04 07:49 AM Re: Rooftop unit follow-up
Mean Gene Offline
Member
Registered: 10/20/03
Posts: 137
Loc: Ohio, USA
I think John's reasoning for it not being a good idea is in the event the chassis of the unit were to become energized or the unit were to catch fire the disco may become untouchable.
Top
#36501 - 04/08/04 08:11 AM Re: Rooftop unit follow-up
Anonymous
Unregistered

Not that it makes it right or wrong but I have mounted a gazillion disco's to RTU's.
Mounted directly to the unit on large units and various strut set-ups on others. The only issues I have had are: Do not mount to access covers. Do not mount over name plates. Do not screw into internal coils .
Top
#36502 - 04/08/04 09:07 AM Re: Rooftop unit follow-up
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
440.14
_________________________
Ryan Jackson,
Salt Lake City
Top
#36503 - 04/08/04 04:15 PM Re: Rooftop unit follow-up
DougW Offline
Member
Registered: 06/08/03
Posts: 1083
Loc: North Chicago, IL
When I worked at a local grocery store chain, I remember seeing several disco's mounted towards the corner of the units - the idea being, if the case becomes "hot", one can D/C the power by using a hot stick / "broom" stick, or other nonconductive means.

The D/C is also visible from 2 sides, and I've seen the units labeled with yellow and black "caution" style labels as to where the D/C's were, as well as information as to which panel they were being fed from.

Not a code requirement, of course, but a good idea nontheless.
Top
#36504 - 04/08/04 04:25 PM Re: Rooftop unit follow-up
triple Offline
Member
Registered: 04/01/02
Posts: 182
Loc: Wisconsin
Kentvw said it best. Follow those directions and you can't go wrong.

If you wire/ground correctly, how can the "case" become hot? If it is not wired correctly then no procedure for disconnect placement is going to make the set-up safe.
Top
#36505 - 04/08/04 04:35 PM Re: Rooftop unit follow-up
maintenanceguy Offline
Member
Registered: 12/02/01
Posts: 303
Loc: Southern NJ, USA
Triple beat me to it. If everything's grounded properly, the disconnect's housing would be hot if the RTU cabinet was no matter how far away it was mounted.

And if it's right on the unit, The HVAC guy (That's usually me) never has to wonder if he's turned off the right switch. And do us a favor, mount your switch right above the equipment's data plate. When they're exposed to the sun and rain they fade so bad we can't read them but everytime I see a data plate under the disco, the plate looks like the day it was made.
Top
#36506 - 04/08/04 04:37 PM Re: Rooftop unit follow-up
triple Offline
Member
Registered: 04/01/02
Posts: 182
Loc: Wisconsin
I do, however, like to mount the disconnect separate from the unit to facilitate that units removal/replacement in the future. Most of the time this is not very practical without a good deal of additional labor. Thus the disco gets screwed to the side of the rooftop unit.
Top
#36507 - 04/08/04 04:48 PM Re: Rooftop unit follow-up
Redsy Offline
Member
Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
I was thinking in terms of replacing the condensing unit, and having the disconnect flopping around on the ground in the meantime.
Top
Page 1 of 2 1 2 >

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Forum Styles
by Admin
01/24/17 02:22 PM
License exam
by TRUE POWER
01/23/17 09:16 PM
Looking for older post
by sparkyinak
01/23/17 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM

Who's Online
1 registered (Admin), 97 Guests and 14 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 08/17/06
Posts: 358

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals