#36433 - 04/06/04 06:01 PM shower light
flush Offline
Member
Registered: 12/14/01
Posts: 12
Loc: nj
i have a bet with my boss.... he says that a light above a tub needs to be gfi protected and i cant find a code that says it has to be . now i would like to say that i think its a good idea that it is gfi protected but if someone could clear this up with a code refrence that would be great ....also do you guys normally do it anyway or not thanks
Top
Work Gear for Electricians and the Trades
#36434 - 04/06/04 07:13 PM Re: shower light
NJwirenut Offline
Member
Registered: 09/15/01
Posts: 806
Loc: Bergen County, NJ
It needs a wet location trim, but GFCI protection isn't required by the NEC.

I usually do it anyway, since a GFCI protected circuit is generally just a few feet away.
Top
#36435 - 04/06/04 07:27 PM Re: shower light
Jps1006 Offline
Member
Registered: 01/22/04
Posts: 615
Loc: Northern IL
Depending on how the bet was worded, your boss may have won. Some towns around me have local ammendments that require GFI. I've worked where they wanted all the bathroom lights GFI.
Top
#36436 - 04/06/04 10:12 PM Re: shower light
DougW Offline
Member
Registered: 06/08/03
Posts: 1143
Loc: North Chicago, IL
I've never had to do it, but I know of AHJ's that have required it...

How does your boss like his coffee and donuts?
Top
#36437 - 04/07/04 05:06 AM Re: shower light
n1ist Offline
Member
Registered: 02/13/02
Posts: 183
Loc: Malden MA
Also, if the instructions require it...
Top
#36438 - 04/07/04 02:14 PM Re: shower light
Electricmanscott Offline
Member
Registered: 01/12/02
Posts: 1457
Loc: Holden, MA USA
As stated NEC does not require it. I have never seen a manufacturer require it. And where I am, an inspector cannot require it. People say it is a good idea, in reality why?
Top
#36439 - 04/07/04 04:43 PM Re: shower light
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1374
Loc: West Jordan, Utah, USA
If the bet was based on pure code I would agree with you.

Quote:
Also, if the instructions require it...
This may or may not be a code requirement, as 110.3(B) only requires that the instructions of the listing and labeling be followed.
_________________________
Ryan Jackson,
Salt Lake City
Top
#36440 - 04/07/04 05:05 PM Re: shower light
NJwirenut Offline
Member
Registered: 09/15/01
Posts: 806
Loc: Bergen County, NJ
Quote:
People say it is a good idea, in reality why?


J. Random Homeowner, standing barefoot in a wet shower stall, trying to change a bulb without turning the switch off first?

[This message has been edited by NJwirenut (edited 04-07-2004).]
Top
#36441 - 04/08/04 06:28 AM Re: shower light
Electricmanscott Offline
Member
Registered: 01/12/02
Posts: 1457
Loc: Holden, MA USA
Stupid is as stupid does.
Top
#36442 - 04/08/04 06:45 AM Re: shower light
Jps1006 Offline
Member
Registered: 01/22/04
Posts: 615
Loc: Northern IL
Yeah, but it is our job to idiot-proof the place isn't it?

That's the only problem with having all these codes and regulations. Although that would be a weak argument, one I'd never try to make. Maybe I should say it is an unfortunate result. People get so used to indusrties engineering every bit of danger out of things they stop thinking for themselves.

I remember being on a job a long time ago asking the guy I was with "how do you know that can be done that way" (All I remember is he making assumptions that if wrong would be dangerous) Instead of giving me an answer like "the instructions say...." or "Well you see, this is how this works.....", his reponse was "they wouldn't make it that way."

I was terrified at the mentality.
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 124 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals