The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

   
Page 1 of 3 1 2 3 >
Topic Options
Rate This Topic
#36330 - 04/04/04 07:26 AM 14-2 on 20 amp circuit
Randy Offline
Member
Registered: 09/25/02
Posts: 26
Loc: Concord, Va.
I posted this subject on the code forum, but would like to get other inputs on it.I've heard different views on using 14-2 soley as a swith leg on a 20 amp circuit. Is this code acceptable or not?
Top
Work Gear for Electricians and the Trades
#36331 - 04/04/04 07:28 AM Re: 14-2 on 20 amp circuit
Randy Offline
Member
Registered: 09/25/02
Posts: 26
Loc: Concord, Va.
sorry, should be "switch" leg...
Top
#36332 - 04/04/04 07:48 AM Re: 14-2 on 20 amp circuit
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
No.
_________________________
Ryan Jackson,
Salt Lake City
Top
#36333 - 04/04/04 09:52 AM Re: 14-2 on 20 amp circuit
Roger Offline
Member
Registered: 05/18/02
Posts: 1779
Loc: N.C.
Randy, we can't change the answers that were given in the Code Forum, they are correct.

Why would you want to do this anyways?

BTW; If you want to edit your post for spelling (I do this more than I want to admit ) just click on this in the top of your post.

Roger
Top
#36334 - 04/04/04 10:16 AM Re: 14-2 on 20 amp circuit
Randy Offline
Member
Registered: 09/25/02
Posts: 26
Loc: Concord, Va.
the reason I would want to do this is the fact that 14-2 is more than capable of handling the load requirement for a single switch leg. to me 12-2 to flip a light on is over kill. Light fixtures have 18 gage on 20 amp circuits and they are handling the very same load.
Top
#36335 - 04/04/04 10:32 AM Re: 14-2 on 20 amp circuit
SteveMc Offline
Member
Registered: 02/05/04
Posts: 61
Loc: Rock Hill, SC
The amperage on the 18 ga. fixture wire is limited by the wattage of the lamp. The switch wire on the other hand willl be loaded with the amperage of all the fixtures connected to it. Therefore, if you have twenty (120v) fixtures with a 100w lamp in each your circuit will be loaded to 16.7 amps and that will be the load on the 14/2 switch leg.

[This message has been edited by SteveMc (edited 04-04-2004).]
Top
#36336 - 04/04/04 01:20 PM Re: 14-2 on 20 amp circuit
CTwireman Offline
Member
Registered: 02/07/02
Posts: 839
Loc: Connecticut, USA
_________________________
Peter
Top
#36337 - 04/04/04 01:39 PM Re: 14-2 on 20 amp circuit
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Instead of considering the load on this switch leg I suggest that we keep it simple.

It is a code violation.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#36338 - 04/04/04 03:07 PM Re: 14-2 on 20 amp circuit
ga.sparky56 Offline
Member
Registered: 11/24/02
Posts: 582
Loc: young harris georgia usa
If there's a fire,and the insurance investigator finds that 14-2 sw.leg,whether or not that was the cause of the fire,that would be all the excuse they'ed need not to pay.

Russell
Top
#36339 - 04/05/04 04:38 PM Re: 14-2 on 20 amp circuit
Sir Arcsalot Offline
Member
Registered: 11/17/03
Posts: 117
Loc: Lynden, Washington
If someone wanted to later add a switched outlet(s) to this same circuit using the existing 14-2 there would certainly be a greater potential for the "in-wall filament" syndrome.

Just my two cents' worth.
_________________________
No wire bias here- I'm standing on neutral ground.
Top
Page 1 of 3 1 2 3 >

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
License exam
by TRUE POWER
48 minutes 0 seconds ago
Looking for older post
by sparkyinak
Today at 12:27 AM
Members: Non-Members: Did you know?
by Admin
Yesterday at 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
1 registered (Admin), 85 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 03/13/07
Posts: 167

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals