The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Yesterday at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 223 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 3 1 2 3 >
Topic Options
Rate This Topic
#36330 - 04/04/04 07:26 AM 14-2 on 20 amp circuit
Randy Offline
Member

Registered: 09/25/02
Posts: 26
Loc: Concord, Va.
I posted this subject on the code forum, but would like to get other inputs on it.I've heard different views on using 14-2 soley as a swith leg on a 20 amp circuit. Is this code acceptable or not?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#36331 - 04/04/04 07:28 AM Re: 14-2 on 20 amp circuit
Randy Offline
Member

Registered: 09/25/02
Posts: 26
Loc: Concord, Va.
sorry, should be "switch" leg...

Top
#36332 - 04/04/04 07:48 AM Re: 14-2 on 20 amp circuit
Ryan_J Offline
Moderator

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
No.
_________________________
Ryan Jackson,
Salt Lake City

Top
#36333 - 04/04/04 09:52 AM Re: 14-2 on 20 amp circuit
Roger Offline
Member

Registered: 05/18/02
Posts: 1779
Loc: N.C.
Randy, we can't change the answers that were given in the Code Forum, they are correct.

Why would you want to do this anyways?

BTW; If you want to edit your post for spelling (I do this more than I want to admit ) just click on this in the top of your post.

Roger

Top
#36334 - 04/04/04 10:16 AM Re: 14-2 on 20 amp circuit
Randy Offline
Member

Registered: 09/25/02
Posts: 26
Loc: Concord, Va.
the reason I would want to do this is the fact that 14-2 is more than capable of handling the load requirement for a single switch leg. to me 12-2 to flip a light on is over kill. Light fixtures have 18 gage on 20 amp circuits and they are handling the very same load.

Top
#36335 - 04/04/04 10:32 AM Re: 14-2 on 20 amp circuit
SteveMc Offline
Member

Registered: 02/05/04
Posts: 61
Loc: Rock Hill, SC
The amperage on the 18 ga. fixture wire is limited by the wattage of the lamp. The switch wire on the other hand willl be loaded with the amperage of all the fixtures connected to it. Therefore, if you have twenty (120v) fixtures with a 100w lamp in each your circuit will be loaded to 16.7 amps and that will be the load on the 14/2 switch leg.

[This message has been edited by SteveMc (edited 04-04-2004).]

Top
#36336 - 04/04/04 01:20 PM Re: 14-2 on 20 amp circuit
CTwireman Offline
Member

Registered: 02/07/02
Posts: 839
Loc: Connecticut, USA
_________________________
Peter

Top
#36337 - 04/04/04 01:39 PM Re: 14-2 on 20 amp circuit
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Instead of considering the load on this switch leg I suggest that we keep it simple.

It is a code violation.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#36338 - 04/04/04 03:07 PM Re: 14-2 on 20 amp circuit
ga.sparky56 Offline
Member

Registered: 11/24/02
Posts: 582
Loc: young harris georgia usa
If there's a fire,and the insurance investigator finds that 14-2 sw.leg,whether or not that was the cause of the fire,that would be all the excuse they'ed need not to pay.

Russell

Top
#36339 - 04/05/04 04:38 PM Re: 14-2 on 20 amp circuit
Sir Arcsalot Offline
Member

Registered: 11/17/03
Posts: 117
Loc: Lynden, Washington
If someone wanted to later add a switched outlet(s) to this same circuit using the existing 14-2 there would certainly be a greater potential for the "in-wall filament" syndrome.

Just my two cents' worth.