The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 257 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#36266 - 04/02/04 10:14 AM splicing
walt Offline
Junior Member

Registered: 04/02/04
Posts: 1
Is it allowed by code to splice the existing circuit conductors in a panel after upgrading the service due to the fact that the conductors are too short to reach the breakers. Does the code allow this or do you have to splice outside the panel in junction boxes then come into the new panel and terminate.

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#36267 - 04/02/04 12:09 PM Re: splicing

You might take a peek at 02 NEC 312.8

#36268 - 04/02/04 03:30 PM Re: splicing
Electricmanscott Offline

Registered: 01/12/02
Posts: 1478
Loc: Holden, MA USA
It is allowed

#36269 - 04/02/04 04:40 PM Re: splicing
George Corron Offline

Registered: 05/16/01
Posts: 728
Loc: Lorton, Va USA
Sometimes to be a historian, ya just gotta be old.

Not THAT many years ago, panels were thinner, along about 12". You may notice this in some of your travels.

We spliced anyway where we just had to. Then the makers, UL, and just 'bout everyone else got together to reconsider the space requirements and we got the 14" panels, JUST for you.

You're welcome

#36270 - 04/02/04 05:21 PM Re: splicing
Bomzin Offline

Registered: 03/25/04
Posts: 27
Loc: Utah
And now they fit between the studs instead of more framing or adding supports. They should have made them wider years earlier. Some of them are just down right miserable to deal with.


#36271 - 04/02/04 05:43 PM Re: splicing
electure Offline


Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
If our favorite historian's still around..
Didn't it used to be prohibited to splice or pass through a panel?
Something about the conductor in a panel terminating in the panel?