The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
1 registered (gfretwell), 129 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#36023 - 03/27/04 04:54 PM FPE sub-panel
jsimontucson Offline
Junior Member

Registered: 03/27/04
Posts: 3
Loc: Tucson, Arizona USA
I recently purchased a house that I am fixing up for resale. I upgraded the service to 200amps and installed new main distribution panel. Approx 70% of the house has been rewired and is being fed by the new panel. Six existing 20 amp circuits are being fed by a federal pacific sub-panel.

For obvious reasons I want to replace the FPE Panel. I want to run these six circuits back to my new main panel rather than replacing the sub-panel. The new panel located 20’ away on the exterior of the house.

I would delete the sub-panel, splice the conductors and run them to the new panel in 1’ EMT

Here are the questions:

Can I just run # 12 THHN for each of these circuits or do I need to derate?

Are there any other pitfalls to this plan??

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#36024 - 03/27/04 07:33 PM Re: FPE sub-panel
Jps1006 Offline
Member

Registered: 01/22/04
Posts: 609
Loc: Northern IL
I see no problem with that plan as long as you'll have a total of 9 wires (2 hots to 1 neutral). I've seen some people here call them edison circuits. NEC calls them multiwire branch circuits and where I come from they call them networks.

If you aren't familiar with these types of circuits and the hazards of wiring them incorrectly then don't do it. You would need (12) wires in which case you'd need to derate.

BTW you could fit those in 3/4" EMT.

Top
#36025 - 03/28/04 06:39 AM Re: FPE sub-panel
rizer Offline
Member

Registered: 01/03/04
Posts: 90
Loc: bradenton ,fl.,usa
i would also add a ground wire for the circuits and pigtail a jumper the junction box(if metal). i'm not sure if one ground wire would be enough for all 6 circuits

Top
#36026 - 03/28/04 06:57 AM Re: FPE sub-panel
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
The extra ground wire is really not necessary, but couldn't hurt.
One ground wire would be enough for 6 circuits or 60 circuits.

Top
#36027 - 03/28/04 04:05 PM Re: FPE sub-panel
Attic Rat Offline
Member

Registered: 12/14/03
Posts: 530
Loc: Bergen Co.,N.J. USA
... Even if he pulls (9) wires in that pipe, doesn't he still have to derate,being that there are more than (3)current carrying conductors in that raceway???
Russ
_________________________
.."if it ain't fixed,don't break it...call a Licensed Electrician"

Top
#36028 - 03/28/04 04:35 PM Re: FPE sub-panel
Jps1006 Offline
Member

Registered: 01/22/04
Posts: 609
Loc: Northern IL
I don't have this suff memorized but I'll have a go...
3-6 80%
7-9 70%
10- ?? 50%

but table 310-16 says # 12 copper thhn is rated for 30 amps. meaning you can put (30 amps times 70% = 21 amps) 21 amps.

The note at the bottom the table is for overcurrent protection.

NEC 99

Okay I did have to look up the table.

Top
#36029 - 03/28/04 04:38 PM Re: FPE sub-panel
caselec Offline
Member

Registered: 04/14/02
Posts: 557
Loc: San Jose, CA
Attic Rat

You are correct. If these circuits are multi-wire circuits the neutrals don’t need to be counted but there will still be 6 current caring conductors. The ampacity of #12 THHN is 30 amps and table 310.15(B)(2)(a) specifies 80% adjustment factor for 4-6 conductors. This would result in the #12 THHN conductors having an ampacity of 24 amps. If these wires are installed in wet locations the starting ampacity of #12 THWN in 25 amps which after applying would result with an ampacity of 20 amps.

Curt
_________________________
Curt Swartz

Top
#36030 - 03/28/04 04:56 PM Re: FPE sub-panel
Attic Rat Offline
Member

Registered: 12/14/03
Posts: 530
Loc: Bergen Co.,N.J. USA
...Thanx guys,..

Jsimontucson,..watch your phasing when using (1)neutral per (2)hots...make sure that each corresponding phase conductor lands on a different phase...otherwise unfavorable imbalances on the neutral leg will result in overheating the neutral..Just group your breakers accordingly..."A" phase for one phase conductor,..and "B" phase for the other, and land the neutral normally..
Russ


[This message has been edited by Attic Rat (edited 03-28-2004).]
_________________________
.."if it ain't fixed,don't break it...call a Licensed Electrician"

Top
#36031 - 03/29/04 08:54 AM Re: FPE sub-panel
classicsat Offline
Member

Registered: 11/23/02
Posts: 449
Why not run ONE neutral, and ONE ground, using the stock neutral and ground bussbars in the original panel? (of course, the neutral appropriately sized)

Top
#36032 - 03/29/04 06:50 PM Re: FPE sub-panel
jsimontucson Offline
Junior Member

Registered: 03/27/04
Posts: 3
Loc: Tucson, Arizona USA
Thank you all verry much for your help.