#35978 - 03/25/04 11:39 PM 8/2 UF  
Anonymous
Unregistered

Has anyone seen 8/2(with ground) UF? I can find 8/3 in UF but only 8/2 in NM.
Thanks, Brian


Work Gear for Electricians and the Trades

#35979 - 03/25/04 11:51 PM Re: 8/2 UF  
Merlin  Offline
Member
Joined: Jan 2004
Posts: 170
NW Indiana
Brian

8/2 UF with ground is available at www.gesupply.com . The part number is 8-2 WG UF RL. I have never used any but it is in my catalog.

Kevin


#35980 - 03/26/04 05:30 AM Re: 8/2 UF  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Brian, can I ask what you are feeding with the 8/2?

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts

#35981 - 03/26/04 10:28 AM Re: 8/2 UF  
Anonymous
Unregistered

Thanks Merlin.
Iwire, it's for a 30A 120V RV hookup. The run is too long for #10.
Brian


#35982 - 03/26/04 05:34 PM Re: 8/2 UF  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Brian if you have a sharp inspector they will notice that grounding conductor is to small.

250.122(B) requires the grounding conductor size to be increased when the other conductors are increased for any reason.

In the case of a 30 amp circuit you need a full size grounding conductor, run 8 AWG hot & neutral and you need a 8 AWG ground.

You might want to use the 8/3 and ask the inspector if he has a problem with remarking the red to green or just stripping the red to bare.

Good luck, Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts

#35983 - 03/27/04 08:18 AM Re: 8/2 UF  
Sandro  Offline
Member
Joined: Dec 2001
Posts: 444
Stoney Creek, ON, Canada
I've never priced 8/2 cable, but would not 8/3 be cheaper as its much more common? Just a thought.


#35984 - 03/27/04 09:28 PM Re: 8/2 UF  
Anonymous
Unregistered

Thanks for the replies. I never thought about the grounding conductor. Guess I'll ask the inspector first, if he balks it will be time for pipe and THHN/THHW.
I've always wondered about re-marking a red, white or black conductor as a grounding conductor and in fact I've done it on occasion however there were no inspections.
What are most AHJ's position on this?



Member Spotlight
richard
richard
L.I. New York
Posts: 94
Joined: August 2003
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.014s Queries: 14 (0.003s) Memory: 0.7766 MB (Peak: 0.9278 MB) Zlib enabled. Server Time: 2017-03-27 16:33:25 UTC