The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

   
Page 1 of 3 1 2 3 >
Topic Options
Rate This Topic
#35690 - 03/19/04 04:13 AM Very strange single line diagram?
electure Offline


Member
Registered: 12/24/00
Posts: 4229
Loc: Fullerton, CA USA
I've never seen a service set up like this one that came in for us to bid.
Is this common in some other part of the country?
Here in Southern CA, it certainly isn't how it's done.








Have any of you seen something like this??...S
Top
Work Gear for Electricians and the Trades
#35691 - 03/19/04 04:35 AM Re: Very strange single line diagram?
ayrton Offline
Member
Registered: 12/21/01
Posts: 205
Loc: Pa
Unless I am missing something, I don't see anything unusual. Only thing I would do different is runn paralell 250's instead of 600's

[This message has been edited by ayrton (edited 03-19-2004).]
Top
#35692 - 03/19/04 04:58 AM Re: Very strange single line diagram?
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 826
Loc: Michigan
They use that in our area . The 1 1/4 is for utility company metering wires. They put the ct's at the transfomer,you then run straight to the main service panel with your service conductors from the transformor. This is only used on larger services.
Top
#35693 - 03/19/04 05:17 AM Re: Very strange single line diagram?
Roger Offline
Member
Registered: 05/18/02
Posts: 1779
Loc: N.C.
Hello Electure, I agree with the others, this a common installation (design) here also.

Roger
Top
#35694 - 03/19/04 05:27 AM Re: Very strange single line diagram?
watthead Offline
Member
Registered: 10/13/01
Posts: 182
Loc: South Carolina
Where do you guys get that 4-1/2" conduit? Do your supply houses stock it or is it special order?
Top
#35695 - 03/19/04 05:56 AM Re: Very strange single line diagram?
Roger Offline
Member
Registered: 05/18/02
Posts: 1779
Loc: N.C.
Hmmmm, I didn't pay attention to that.

Come to think of it, with a conflict between the notes and reality, it's actualy a more common design than I first thought.

Roger

[This message has been edited by Roger (edited 03-19-2004).]
Top
#35696 - 03/19/04 06:43 AM Re: Very strange single line diagram?
Anonymous
Unregistered

Is your question about the metering set up? I see this on "canned" drawings where the E.E. is from a different state and the job is for a nation wide chain type store. So then the question becomes - How do I bid this and stay competitive? Include the C.T. can, C.T.'s labor etc. or not? I have bid this type of set up per drawings with an adder to meet local requirements.
Top
#35697 - 03/19/04 08:13 AM Re: Very strange single line diagram?
Megawatt Offline
Member
Registered: 03/11/04
Posts: 74
Loc: Lexington,Ky, USA
Most often the POCO will furnish the 13 terminal Meterbase for the CT installation, you would just have to mount it on some 2" Rigid & Strut. As for the conduit, I would also parallel conductors & use a smaller, more common size of conduit. Watch the price of the copper though, it has been going up lately, & could change quickly.
Top
#35698 - 03/19/04 08:42 AM Re: Very strange single line diagram?
earlydean Offline
Member
Registered: 12/22/03
Posts: 749
Loc: Griswold, CT, USA
The POCO will dictate where the metering enclosure is to be mounted. If you have never seen it like that before (me neither) then you need to check with the POCO as to where they accept the CT meter. Out here (New England) we have to purchase and install a separate CT/PT enclosure, usually as part of the main disconnect, then the meter can is remotely mounted outside the building.

4-1/2 inch conduit? I've never run across it before. Maybe it is metric, then rounded off?
_________________________
Earl
Top
#35699 - 03/19/04 01:24 PM Re: Very strange single line diagram?
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
The 4 1/2" conduit seems a little strange.

As earlydean has said in our area the metering CTs would be inside, I tried to get the local POCO go with this setup before due to space limitations in the building, they said they do not want metering at the transformer in case a replacement is needed they won't have to get the metering guys involved with the swap out.

ayrton and Megawatt, this appears to me to be a 1,200 amp service, 3 sets of 600s, assuming copper.

Are you saying you would rather run 5 sets of 250s in place of 3 sets of 600s?

Why?, more time more material.

I would not try or want to use smaller cable 600 kcmil is great in 3 1/2" conduit.

My wild guess is that Note 4 should read.

"4) PROVIDE 3 SETS 4 #600KCMIL-3 1/2" C"

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
Page 1 of 3 1 2 3 >

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
License exam
by TRUE POWER
01/23/17 09:16 PM
Looking for older post
by sparkyinak
01/23/17 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
1 registered (Admin), 64 Guests and 13 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 11/11/05
Posts: 190

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals