#35642 - 03/18/04 07:33 AM Never seen before NM-B cable
aninspect Offline
Junior Member
Registered: 01/29/04
Posts: 7
Loc: Phoenixville, PA.
The other day I came across some NM-B cable, 8-3 w/g, which had wires which all had black insulation and were numbered one, two and three.

Is what struck me as odd, was that the insulation on all the wires was black, no white/gray for the neutral and bare/green for the grounding wire.

While I could not manipulate the wire enough to read the words NM-B, I could read the words 8-3 w/g and the outer coverings were consistent with sheathed cable.

Has anyone ever seen this before, or know anything about the source of the wire?

Thanks,

Joe Myers
_________________________
Joe Myers
A & N Inspections, Inc.
Phoenixville, PA 19460
Top
Work Gear for Electricians and the Trades
#35643 - 03/18/04 07:50 AM Re: Never seen before NM-B cable
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
Sounds like you have some "tray cable" to me.
Don
_________________________
Don(resqcapt19)
Top
#35644 - 03/18/04 10:58 AM Re: Never seen before NM-B cable
CDN_ELECTRICIAN Offline
Member
Registered: 01/22/03
Posts: 73
Loc: Concord,Ontario,Canada
Found this for you thought you be interested!
http://www.faqs.org/faqs/electrical-wiring/part2/section-5.html
Top
#35645 - 03/18/04 11:01 AM Re: Never seen before NM-B cable
Bjarney Offline
Moderator
Registered: 04/10/02
Posts: 2527
Loc: West-Southern Inner-Northeast ...
I think it may be tray cable, too.
http://www.houwire.com/catalog/technical/color_code.asp
ICEA/NEMA Method 4 – A neutral- or single-colored insulation compound is surface ink printed with conductor number to provide positive conductor identification through 21 conductors.
Top
#35646 - 03/18/04 12:04 PM Re: Never seen before NM-B cable
Bjarney Offline
Moderator
Registered: 04/10/02
Posts: 2527
Loc: West-Southern Inner-Northeast ...
Aside — 99 NEC 200-6(e) and 250-119(c) seem to correspond with the multiconductor-cable “no white or green” individual-conductor coding to be field-reidentified as grounded and grounding conductors… with the usual disclaimer ”where conditions of maintenance and supervision ensure that only qualified persons will service…”
Top
#35647 - 03/18/04 07:23 PM Re: Never seen before NM-B cable
aninspect Offline
Junior Member
Registered: 01/29/04
Posts: 7
Loc: Phoenixville, PA.
Thank you everyone, I appreciate the help. I have never run across any tray cable before, so it looks like that may be my answer.

Has anyone ever seen or heard of this stuff in a number 8 stranded?

Second question. Is the sheathing on tray cable like that of NM-B cable?

Joe Myers
_________________________
Joe Myers
A & N Inspections, Inc.
Phoenixville, PA 19460
Top
#35648 - 03/18/04 07:49 PM Re: Never seen before NM-B cable
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
Joe,
Tray cable comes in all sizes from #18 or smaller to 500kcmil and larger. It can have 2 to more than 50 conductors. It comes with or without grounding conductors. Some is color coded and other is numbered on all black conductors. Most of it that I have seen has a black outer jacket and a very close resemblance to NM.
Don

[This message has been edited by resqcapt19 (edited 03-18-2004).]
_________________________
Don(resqcapt19)
Top
#35649 - 03/18/04 09:05 PM Re: Never seen before NM-B cable
Bjarney Offline
Moderator
Registered: 04/10/02
Posts: 2527
Loc: West-Southern Inner-Northeast ...
Type TC typicals.. http://www.houwire.com/catalog/products.asp?catid=45 http://www.houwire.com/catalog/products.asp?catid=46
N.B.: “Color Code: Power Sizes: ICEA Method 4”

[One rare occasions, TC may be found 'fished' into walls.]
Top
#35650 - 03/19/04 08:28 AM Re: Never seen before NM-B cable
aninspect Offline
Junior Member
Registered: 01/29/04
Posts: 7
Loc: Phoenixville, PA.
Don,

Thanks for the reply. I have never seem cable tray before, so this is a new one on me. Is this stuff pretty common? Meaning, do you use it, or see it a lot?

BJarney,

Thanks for the links. I had read previously after it was suggested this maybe tray cable, that this stuff is suitable for direct buriel, now I am sure that it is. That would make good sense since this was servicing a sub panel in a detached garage and I could not verify it was running in conduit to the garage.

Thanks,

Joe Myers
_________________________
Joe Myers
A & N Inspections, Inc.
Phoenixville, PA 19460
Top
#35651 - 03/19/04 10:31 AM Re: Never seen before NM-B cable
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
Joe,
It is a very common industrial wiring method.
Don
_________________________
Don(resqcapt19)
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 04/03/02
Posts: 6778
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 70 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals