The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
Trumpy 8
sparkyinak 7
Who's Online
0 registered (), 81 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#35014 - 03/02/04 04:35 PM 200A service
marixelectric_dfw Offline
Member

Registered: 03/01/04
Posts: 11
Loc: Tracy, Ca
i have a new customer who is building a 4700 sq. ft. home with a pool and spa. he also plans to build a pool/guest house of about 1000 sq.ft. he insists on only having a 200A service. i told him that thr load calcs say he needs a 400A service. now he thinks im trying to get over. Am i correct and he's just a moron?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#35015 - 03/02/04 05:39 PM Re: 200A service
Roger Offline
Member

Registered: 05/18/02
Posts: 1779
Loc: N.C.
For a true evaluation you will have to show us how you arived at your calculations.

Roger

Top
#35016 - 03/02/04 09:16 PM Re: 200A service
Lesmcw Offline
Junior Member

Registered: 02/09/04
Posts: 5
Loc: Canada
Here is a link you can try. It is Canadian, but hey...demand is demand for a quick reference. http://www.codemath.com/cgi-bin/Run.pl?script=Cec8_200

Top
#35017 - 03/03/04 07:20 AM Re: 200A service
C-H Offline

Member

Registered: 09/17/02
Posts: 1508
Loc: Stockholm, Sweden
That's a neat calculator. Just for fun I punched in the numbers for a known house and it came back with a demand of 21kW. (Not really relevant as I'm in Europe, but hey demand is demand ) What kind of service would you use for this in US/Canada?

Top
#35018 - 03/03/04 06:26 PM Re: 200A service
marixelectric_dfw Offline
Member

Registered: 03/01/04
Posts: 11
Loc: Tracy, Ca
the service is for the us

Top
#35019 - 03/04/04 07:33 PM Re: 200A service
Lesmcw Offline
Junior Member

Registered: 02/09/04
Posts: 5
Loc: Canada
We'd use a minimum 100 amp service for a 21 Kw (88 amp)house demand load. (Canada)

Top