The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
Yesterday at 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 267 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#34987 - 03/01/04 01:11 PM Size of a main breaker/disconnect.
Edward Offline

Registered: 12/14/02
Posts: 309
Loc: California
I have to bid on a complete rewire and services and subpanel upgrades for two complexes. One is a 3 single unit complex and other is a 4 single unit complex. Each individual unit is about 800sqft.
My questios is can i treat this as one main 200Amp disconnect with 3 or 4 60 amp individual mains?
If not can i use the standard load calculation for each unit and add it all up to see what my main will be?

PS. It is all gas heater and cooking appliance. One laundry unit for both buildings.


Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#34988 - 03/01/04 01:24 PM Re: Size of a main breaker/disconnect.
earlydean Offline

Registered: 12/22/03
Posts: 749
Loc: Griswold, CT, USA
You have to do both.
Each individual unit must have it's feeder calculated, and the building must have it's size calculated for the entire building loads.