The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 198 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#34976 - 03/01/04 07:13 AM disconect size
drgnz23 Offline
Member

Registered: 02/17/02
Posts: 56
Loc: los angeles
hey guys i have an air compressor that needs to be hooked up. Its a 7hp 240 volt single phase motor.The nameplate has an amp reading of 23amps .What is the proper way to size for the disconect? Can you please help this rookie.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#34977 - 03/01/04 07:18 AM Re: disconect size
Ryan_J Offline
Moderator

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
Take a look at 430.6(A)(1), and see that it refers you to the tables. Table 430.148 will be the table that governs. It looks like it will be slightly less than 40 amps, therefore a sixty amp disconnect will be required, fused properly to protect the conductors.

[This message has been edited by Ryan_J (edited 03-01-2004).]
_________________________
Ryan Jackson,
Salt Lake City

Top
#34978 - 03/01/04 08:22 AM Re: disconect size
drgnz23 Offline
Member

Registered: 02/17/02
Posts: 56
Loc: los angeles
why is it the the wire going to the motor are so small? They look to be about 10 awg?

Top
#34979 - 03/01/04 08:28 AM Re: disconect size
Ryan_J Offline
Moderator

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
The motor probably has internal overlaod protection. If you look at the running load amps of the motor, you will see that the #10 will carry the load.
_________________________
Ryan Jackson,
Salt Lake City

Top
#34980 - 03/01/04 01:14 PM Re: disconect size
earlydean Offline
Member

Registered: 12/22/03
Posts: 749
Loc: Griswold, CT, USA
The insulation on motor conductors is different from the building conductors, and can handle more current without damaging the insulation.
Table 430.148 shows 40 amps for a 7-1/2 HP motor. Interploating for a 7 HP motor, I get 37.6 amps. Table 310.16 gives me (at 125% per 430.22 that's 47 amps)#8 copper wires. 60 amp disconnects are standard size.
The only place the 23 amps is used is for the heaters. Use overloads in your magnetic or manual starter from the FLC found on the nameplate. See 430.43(C) for allowed oversizing.

Earl
_________________________
Earl

Top
#34981 - 03/02/04 12:50 AM Re: disconect size
drgnz23 Offline
Member

Registered: 02/17/02
Posts: 56
Loc: los angeles
after running the compressor i get about 12 amp per leg....i think i need to go back an install a bigger disco. my wire size is good and so is my breaker but im still having trouble reading the code book . Why cant they make it easiear to understand?

Top
#34982 - 03/02/04 08:42 AM Re: disconect size
winnie Offline
Member

Registered: 09/15/03
Posts: 652
Loc: boston, ma
Ryan_J,

Isn't there an exception inf 430.6 for appliances that include motors, where you get to use the nameplate amp rating _of the appliance_ rather than the table value?

drgnz23,

The wire _inside of an appliance_ is rated under different rules than the wire used for running circuits in walls. This is because wire is not limited by _current_, but is instead limited by temperature. The temperature is caused by _heat_, which is produced when current flows, and _heat disspiation_, which depends upon the surroundings. When you have a better idea of the heat dissipation available, you can use thinner wire, and the UL listing (not the NEC) determines what wire is appropriate in an appliance.

If you calculate out the values in table 430.148, the VA of the circuits required is roughly _double_ the wattage of the motors described (1 hp is 746 watts). This doubling is required because of inefficiency, power factor, and overload requirements. With an appliance, all of these factors are better controlled than with a general purpose motor.

If possible, you should consult the manufacturer of the appliance. They may have a recommended or required conductor ampacity, disco size, and OCPD requirement. This should be reflected on the nameplate, but the instruction manual is probably a clearer source.

Lastly, the current reading that you get when running the compressor will depend upon the load on the motor; in particular the pressure in the tank. The higher the pressure, the more work the motor will do, and the greater the current. I can tell you right now that 12A at 240V is _not_ 7hp, but less than half that depending upon power factor and efficiency.

-Jon

Top
#34983 - 03/02/04 09:46 PM Re: disconect size
drgnz23 Offline
Member

Registered: 02/17/02
Posts: 56
Loc: los angeles
winnie . You beat me to it after a long stare at da book i found the exception you are mentioning. Ive been trying to learn and do from the nec code book as much as possible you guys have been great help.

Top
#34984 - 03/03/04 06:20 AM Re: disconect size
winnie Offline
Member

Registered: 09/15/03
Posts: 652
Loc: boston, ma
drgnz23,

Before you trust the 'exception' interpretation, please let the more experienced chaps chime in on it. I am here learning code as well

-Jon

Top
#34985 - 03/03/04 12:58 PM Re: disconect size
Jps1006 Offline
Member

Registered: 01/22/04
Posts: 609
Loc: Northern IL
For sizing disconnects I usaully rely on the HP rating. Instead of ordering a 60 amp disconnect, ask them for a 7-1/2 HP at 240 volt disconnect. The manufaturer does all the sizing for you.