#3491 - 08/20/01 12:06 PM A question
kent Offline
Member
Registered: 08/16/01
Posts: 27
Loc: Sweden
When you want to control lights from two different places (e.g. the top and bottom of a stairwell) you have two different ways of doing it (pic A and B). Some guy told me that B was the American way. Is that right?




[This message has been edited by Webmaster (edited 08-20-2001).]
_________________________
Fuseman
Top
Work Gear for Electricians and the Trades
#3492 - 08/20/01 01:08 PM Re: A question
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 4196
Loc: NY, USA
Kent,

(I hope you don't mind, I had to edit your post to get the picture displayed)

A is the way I've always seen and done it.
(We call it 3 way switching)

I'd have to sit down and look at B for awhile to even figure out what's going on there! Gotta go for now though.

Bill
Top
#3493 - 08/20/01 01:49 PM Re: A question
Anonymous
Unregistered

A is normal and correct. B is is unusual and confused me at first glance too. But see my follow up comments below.


[This message has been edited by Dspark (edited 08-20-2001).]
Top
#3494 - 08/20/01 02:15 PM Re: A question
sparky Offline
Member
Registered: 10/18/00
Posts: 5545
Top
#3495 - 08/20/01 03:52 PM Re: A question
Anonymous
Unregistered

Perhaps someone was just trying to insult Americans by making it far more complicated than it needs to be.
Top
#3496 - 08/20/01 04:47 PM Re: A question
Tom Offline
Member
Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
Diagram B looks like something you would see in a Knob & Tube installation. I've also heard it called a "California 3 way."

Tom
_________________________
Few things are harder to put up with than the annoyance of a good example.
Top
#3497 - 08/20/01 05:30 PM Re: A question
sparky Offline
Member
Registered: 10/18/00
Posts: 5545
http://www.hometoys.com/htinews/apr98/articles/kingery/kingery8.htm

yuppy, Tom is right...

it would be a version of fig#7 in the above link. refered to as a 'french 3-way' .
I have heard it refered to as a 'Chicago 3-way'

actually Kent, the guy who told you it was an American version is right, but it has not been in use for a long time.
It would be hard, in fact, to find a field electrician that actually has installed K&T as a beginner, most are probably retired.

It's comical how these boo-boo's gain names of localities....



[This message has been edited by sparky (edited 08-20-2001).]
Top
#3498 - 08/20/01 05:39 PM Re: A question
Anonymous
Unregistered

>yuppy, Tom is right...
Nopey. It is nothing like figure #7.

>Diagram B looks like something you would see in a Knob & Tube installation.
That could be.

>I've also heard it called a "California 3 way."
No, I think the [Chicago/California/French/etc] three-way is the one with the switched neutral.

I hereby retract my earlier comment that about a Code violation.

I have flattened out the diagram into four parallel lines (one runs only half way). Except for the fact that four wires are required rather than three, it has no problems that I can see.

I wish I could post my redrawing of it.
Top
#3499 - 08/20/01 05:50 PM Re: A question
Anonymous
Unregistered

On a sheet of paper:

1. Draw three parallel horizontal lines and label them as L, T1, T2 from top to bottom.

2. Draw a fourth parallel line under line T2 from the left but of half the length of the previous three and label it N.

3. Install a luminaire between the mid-point of T2 and the end of N directly under this point of T2.

4. Install a three-way switch at each end of T1 (as the common) with each switching between L and T2.

5. Observe that there are no safety violations with this scheme. It simply requires about 1 to 33% more wire.
Top
#3500 - 08/21/01 10:52 AM Re: A question
pauluk Offline
Member
Registered: 08/11/01
Posts: 7693
Loc: Norfolk, England
Both methods are in use in the U.K., depending mainly upon the physical wirng layout.

(A) is the "traditional" method, used almost universally in the past where junction boxes were used to wire up lighting circuits.

(B) is common now, as many houses have lights wired on the "loop-in" principle to avoid the jct-boxes (i.e. permanently live power is taken to the light fitting and a separate cable runs from there to the switch).

With this method an extra jct-box is avoided, as a 3-way (plus gnd) cable then just runs from one switch to the other. Less work in the roof space, but more cable.

It's also known as the "conversion" method here, as it's an easy way to change a normal single switch to 2/3-way operation.
Top
Page 1 of 2 1 2 >

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM
Looking for older post
by Texas_Ranger
01/21/17 03:22 PM
Last time to chat here
by Trumpy
01/20/17 11:41 PM

Who's Online
3 registered (gfretwell, TRUE POWER, Admin), 123 Guests and 12 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Tom
Tom
Member Since: 01/01/01
Posts: 1069

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals