The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
12/08/16 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 8
Trumpy 6
Who's Online
0 registered (), 214 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#34588 - 02/16/04 02:03 PM control transformer
jbfan Offline
Member

Registered: 02/21/03
Posts: 75
Loc: Newnan, GA
Do I need to bond the neutral of a 208v to 120v control transformer. The panel that feeds the transformer has the ground and neutral bonded inside the panel. It is a 500va transformer.

Thanks
_________________________
"Yes I am a Pirate, 200 years to late" Jimmy Buffett

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#34589 - 02/16/04 02:30 PM Re: control transformer
golf junkie Offline
Member

Registered: 04/22/01
Posts: 511
Loc: York, NE
No, You can bond it or let it float at your option. I prefer to bond it...it makes voltage reading to ground more meaningful, makes troubleshooting easier.

GJ

[This message has been edited by golf junkie (edited 02-16-2004).]

Top
#34590 - 02/16/04 03:53 PM Re: control transformer
Bjarney Offline
Moderator

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
Please consider grounding the 120V-secondary winding. For 1000VA-and-under control-power transformers, NEC 250-30 allows the winding to be grounded with a simple 'case' jumper. The usual full-tilt grounding-electrode/building-steel connection is not needed. This is a real easy way to keep electrostatically-induced garbage off the control circuit.




[This message has been edited by Bjarney (edited 02-16-2004).]

Top
#34591 - 02/16/04 04:53 PM Re: control transformer
jbfan Offline
Member

Registered: 02/21/03
Posts: 75
Loc: Newnan, GA
Thanks for the answers. It will be bonded tomorrow!
_________________________
"Yes I am a Pirate, 200 years to late" Jimmy Buffett

Top
#34592 - 02/16/04 06:19 PM Re: control transformer
Scott35 Offline

Broom Pusher and
Member

Registered: 10/19/00
Posts: 2724
Loc: Anaheim, CA. USA
I second Bjarney's suggestion!



Scott35
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!