The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Today at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
Yesterday at 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Texas_Ranger 8
Trumpy 8
sparkyinak 7
Who's Online
0 registered (), 218 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#34522 - 02/14/04 10:24 AM Compressor Amp Draw
golf junkie Offline
Member

Registered: 04/22/01
Posts: 511
Loc: York, NE
Does anyone have a chart for rule of thumb amperage draws on HVAC and refrigeration compressor based on tonnage??

For instance how many amps does a 208v, 3ph, 5 ton compressor draw?

GJ

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#34523 - 02/14/04 11:05 AM Re: Compressor Amp Draw
Jps1006 Offline
Member

Registered: 01/22/04
Posts: 609
Loc: Northern IL
Obviously you are looking for a way to estimate site unseen for ball-parking a bid or having some idea for sizing something. Just thought I'd say that before you get "You really should size it off the nameplate rating".

I don't know off hand for your example, but I've found for single phase 240 volt, about 10 amps per ton. That's breaker size. 5 ton 50 amp breaker, etc.

Top
#34524 - 02/14/04 12:02 PM Re: Compressor Amp Draw
golf junkie Offline
Member

Registered: 04/22/01
Posts: 511
Loc: York, NE
Jps,
You are correct, I'm looking for a ballpark estimate. The final circuit sizing will be done from the nameplate info.

We are running to more and more requests where people are trying to save on the engineering. Tough to bid when it's all rather undefined.

I found a conversion that says 1 ton=4.71HP. Going back to my example then I calculate;

5 ton = 5 x 4.71 = 23.55hp

The amp draw for that doesn't come close to matching carrier's data for a 5 ton RTU. Carrier says that a 5 ton RTU 208v, 3ph, has a FLA of 32A.

????????????????

Top
#34525 - 02/14/04 01:57 PM Re: Compressor Amp Draw
wolfdog Offline
Member

Registered: 10/24/01
Posts: 135
Loc: Dallas,TX
12,000 BTU (1 ton) = 4.7161 horsepower hour as a raw calcultion with formulas.

It does not translate into hp/ton on small equipment.

Top