#34424 - 02/11/04 04:35 AM Why a continuous ground?
Big A Offline
Member
Registered: 01/22/03
Posts: 46
Loc: Lynchburg, VA
Does anybody know why a system has to have a continuous ground? I understand why you would need it in things that were close together but I don't understand why if I have a feed on one side of the street, and a metal cabinet on the other side of the street, these must have a continuous ground. Seperate grounds are not allowed.

Any reasons why?
Top
Work Gear for Electricians and the Trades
#34425 - 02/11/04 04:50 AM Re: Why a continuous ground?
Attic Rat Offline
Member
Registered: 12/14/03
Posts: 524
Loc: Bergen Co.,N.J. USA
...So that it can never be disconnected,or the lugs,bugs,etc..become loose and create a high resistance to ground.
AR
_________________________
.."if it ain't fixed,don't break it...call a Licensed Electrician"
Top
#34426 - 02/11/04 05:22 AM Re: Why a continuous ground?
earlydean Offline
Member
Registered: 12/22/03
Posts: 751
Loc: Griswold, CT, USA
To facilitate the operation of the OC device you need a low impedance fault path back to the OC device.
_________________________
Earl
Top
#34427 - 02/11/04 11:08 AM Re: Why a continuous ground?
Big A Offline
Member
Registered: 01/22/03
Posts: 46
Loc: Lynchburg, VA
So the OCP will not function with a seperate ground? I guess that makes sense, but wouldn't the difference of potential between the two grounds have to be some huge (say 1 meg ohm) difference?
Top
#34428 - 02/11/04 11:25 AM Re: Why a continuous ground?
winnie Offline
Member
Registered: 09/15/03
Posts: 649
Loc: boston, ma
Lets say, for example, that the grounding electrode on that remote box had a resistance of 25 ohms. Let us further stipulate that the grounding electrode system on the main panel has a resistance of 15 ohms. You get a dead 'hot to ground' short on the remote box, but you don't have any equipment grounding conductor in the feed to the box. Finally, presume that this is a single phase 120V to ground circuit.

Net result: 3A of current flowing through the ground. The remote box is sitting at 75V to ground, and the circuit breaker won't trip. All you've done is created a shock hazard and wasted electricity heating the earth.

Note: 'Resistance to ground' of a grounding electrode is something of a made up number. You presume that the earth as a whole is a perfect conductor, and then attribute any resistance to current flow to the grounding electrode. But in reality the earth is a real conductor with real resistance, and the distance between your electrodes will matter. Imagine that your two electrodes were driven into the ground parallel to each other and 1cm apart. Clearly the resistance between the electrodes will be lower than the overall resistance to earth. But the approximation is good for electrodes spaced significantly greater than their size.

-Jon
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 94 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals