#34007 - 01/30/04 08:41 PM Load Center Location
BarBeQue Offline
Junior Member
Registered: 01/30/04
Posts: 7
Loc: Rainelle, WV USA
Howdy folks. I have a friend that wants me to upgrade his 60 amp service to a norman 200 amp. His current box is located on the side of his house. I said this is a problem, so he asks me if I can put it in his screened in back porch. ummmmm???? I told him i'd have to find out.
Top
Work Gear for Electricians and the Trades
#34008 - 01/31/04 05:49 AM Re: Load Center Location
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
it's cheaper to install a panel close to the original location , simply in terms of junction boxes.

but if you need to turn the location inside out (assuming it's in a noncompliant 110.26 place now) go with a nema 3R setup...

~S~
Top
#34009 - 01/31/04 03:42 PM Re: Load Center Location
BarBeQue Offline
Junior Member
Registered: 01/30/04
Posts: 7
Loc: Rainelle, WV USA
What is a Nema 3R setup? Directly on the other side of the wall is his living room and he doesnt want it placed in there. Other than on his screened in back porch, he would like to have it on in his closet. But the back porch would be an easier move. Is it legal?
Top
#34010 - 01/31/04 05:36 PM Re: Load Center Location
earlydean Offline
Member
Registered: 12/22/03
Posts: 751
Loc: Griswold, CT, USA
NEMA 3R is raintight
It would be OK in the screened porch, so long as nothing would be stored in front of the panel. In the closet is usually not OK, unless the closet is dedicated electrical, or huge. There must be a 36" deep x 30" wide area in front of the panel, kept clear at all times for access. 110.26
Best option, IMHO is to buy the raintight panel.
Earl
_________________________
Earl
Top
#34011 - 01/31/04 06:49 PM Re: Load Center Location
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
If it's a clothes closet, it's never OK to put a panel in it: 240.24(D)
"Not in Vicinity of Easily Ignitible Material
Overcurrent device shall not be located in the vicinity of easily ignitible material, such as in clothes closets"
(Why is it a problem on the side of the house?)...S


[This message has been edited by electure (edited 01-31-2004).]
Top
#34012 - 01/31/04 11:42 PM Re: Load Center Location
wewire2 Offline
Member
Registered: 11/14/02
Posts: 244
Loc: California
If it is a meter panel, the location has to be approved by the serving utility.
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 45 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals