#33496 - 01/22/04 03:30 PM lens cover for shower lights?
mj Offline
Member
Registered: 06/10/02
Posts: 186
Loc: meriidian, ms
any exceptions for not having the lens cover for a fixture located over a shower ?is this per (nec) or (ahj) rule ?
Top
Work Gear for Electricians and the Trades
#33497 - 01/22/04 03:42 PM Re: lens cover for shower lights?
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1374
Loc: West Jordan, Utah, USA
410.4(A) addresses luminiares in wet and damp locations. The location that you describe is a damp one, and therefore the fixture must be listed as such. The only way (that I'm aware of) to obtain this is with a shower lens.

[This message has been edited by Ryan_J (edited 01-22-2004).]
_________________________
Ryan Jackson,
Salt Lake City
Top
#33498 - 01/22/04 04:01 PM Re: lens cover for shower lights?
mj Offline
Member
Registered: 06/10/02
Posts: 186
Loc: meriidian, ms
Ryan, a saleman came to my office today with a fixture...(progress lighting) he stated the fixture is listed for wet locations (no cover required) I have always installed covers over shower lights.
Top
#33499 - 01/22/04 05:49 PM Re: lens cover for shower lights?
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1374
Loc: West Jordan, Utah, USA
Thats interesting.

I would ask to see the UL information on it before I put one up. Oh, by the way, it would be a good idea to keep some copies of that info on the job and in the truck, because I'm sure your inspector will ask for it.....I would!

Let us know what you find, would you?
_________________________
Ryan Jackson,
Salt Lake City
Top
#33500 - 01/22/04 08:51 PM Re: lens cover for shower lights?
russ m Offline
Member
Registered: 02/22/03
Posts: 169
Loc: Burbank,IL,USA
I looked up a few reccessed light fixtures on line, and all the ones I found were approved for damp areas with out a cover.
Before I found this I was of the opinion that outdoor reccessed lights had to have closed covers. I've changed my mind.
I think the shower could be a wet location if the ceiling/light fixture is low enough to have water splash into it. Then according to 410.4 it would require a closed trim
Top
#33501 - 01/23/04 12:59 PM Re: lens cover for shower lights?
earlydean Offline
Member
Registered: 12/22/03
Posts: 751
Loc: Griswold, CT, USA
I would look at the configuration of the shower. Many of the smaller shower stalls will have splashing water directed into any fixture inside the stall. I would require a watertight fixture cover for these conditions of use. If, however, there is no way for water to be directed into the fixture, then a fixture approved for damp locations would be approved.
_________________________
Earl
Top
#33502 - 01/23/04 02:37 PM Re: lens cover for shower lights?
rizer Offline
Member
Registered: 01/03/04
Posts: 91
Loc: bradenton ,fl.,usa
c'mon guys any shower should have a lense that is water tight. all it would take is one fool tossing water in the air to create an electrifiing experience.
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 46 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Stack, Scotto, Freecrowder, clee512, Jdscott2005

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals