The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 235 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#33146 - 01/13/04 12:47 PM wire capacity of 1/2 inch conduit
cpalm1 Offline
Member

Registered: 01/06/04
Posts: 62
i have a 1/2 inch conduit that runs from my panel to the far side of my house and supplies 2 rooms, a hallway and a garage.
currently this pipe contains three 15 amp circuits and a 20 amp circuit. these are multiwire circuits. there are 4 14 gague wires and 2 12 gauge wires.

could i add an additonal 2 amp circuit? to do this i would need to pull an additonal 12 gauge wire and a 14 gague neutral.

then i would have 4 15 amp circuits and 2 20 amp circuits.

simply put, the pipe would contain 6-14 AWG (4 current carrying) and 3 12 AWG (2 current carrying) would this be ok, or would the pipe be over stuffed?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#33147 - 01/13/04 01:21 PM Re: wire capacity of 1/2 inch conduit
George Offline
Member

Registered: 02/23/02
Posts: 380
It appears that the answer is you can not, but I just did a rough calculation.

Top
#33148 - 01/13/04 01:35 PM Re: wire capacity of 1/2 inch conduit
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
What is the wire type? If it is THHN there is not a problem with the conduit fill or with the ampacity adjustment for more than 3 current carrying conductors.
Don
_________________________
Don(resqcapt19)

Top
#33149 - 01/13/04 04:25 PM Re: wire capacity of 1/2 inch conduit
cpalm1 Offline
Member

Registered: 01/06/04
Posts: 62
The wire is THHN

Top
#33150 - 01/13/04 06:52 PM Re: wire capacity of 1/2 inch conduit
Jim M Offline
Member

Registered: 08/10/01
Posts: 453
Loc: Chestertown, MD, USA
Why would you pull a 14 ga. neutral with a 20 ga. hot?

Top
#33151 - 01/13/04 07:01 PM Re: wire capacity of 1/2 inch conduit
cpalm1 Offline
Member

Registered: 01/06/04
Posts: 62
because the there is a multiwire system in the pipe that has a 20 amp and 15 amp circuit. when i add the second 20 amp, i plan to use the 12 gauge neutral that is already in the box, and pull a new neutral for the old 15 amp ciruit that is currently sharing the old 20 amp circuit's neutral.

Top
#33152 - 01/13/04 07:04 PM Re: wire capacity of 1/2 inch conduit
cpalm1 Offline
Member

Registered: 01/06/04
Posts: 62
basically i would end up with a total of 5 circuits. there would be 3 15 amp circuits. 2 of them would share a neutral and one would have it's own neutral (the 14 gauge that i am pulling). The new hot 12 gauge would be hooked up to the old 12 gague neutral. of course i would make sure all of the breakers for the multiwire circuits are on opposite 120V legs.