The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Today at 02:39 AM
Photo Upload Tutorial
by DanK
Yesterday at 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 102 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#33134 - 01/13/04 12:18 PM Common Neutral Code ? 215.4 in 2002 NEC
Rob Offline
Member

Registered: 12/22/03
Posts: 15
Loc: New York
How many circuits can one neutral share?
#12 stranded wire.
Code wording is unclear to me, it reads -
TWO or THREE sets of 3-wire feeders or TWO
sets of 4-wire or 5-wire feeders.

(Can I share a common neutral with three 20 amp single phase circuits?)Thanks in advance.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#33135 - 01/13/04 12:33 PM Re: Common Neutral Code ? 215.4 in 2002 NEC
cpalm1 Offline
Member

Registered: 01/06/04
Posts: 62
on single phase you can share a common neutral with 2 circuits of the same ampacity as the neutral. for example, two 20 amp circuits can share one 12 gauge neutral. The catch is that the 2 circuits must be on OPPOSITE legs of the 240 volt breaker panel. The neutral will only carry the differnece in current between the two circuits. for exampl, if one circuit has a 12 amp toaster on it and the other has a 9 amp coffee maker, the neutral will be carrying 3 amps

Top
#33136 - 01/13/04 02:22 PM Re: Common Neutral Code ? 215.4 in 2002 NEC
DougW Offline
Member

Registered: 06/08/03
Posts: 1083
Loc: North Chicago, IL
Don't forget the requirement of D/C'ing BOTH current carrying conductors with one motion (tied OCPD's) for the circuit in questions.

Top
#33137 - 01/13/04 02:54 PM Re: Common Neutral Code ? 215.4 in 2002 NEC
hbiss Offline
Member

Registered: 12/16/03
Posts: 893
Loc: Hawthorne, NY USA
Doug, that only applies if the two circuits supply device(s) on one yoke such as split wired duplex receptacles. (210.4) If this is simply a 3 wire home run then a two pole breaker is not required.
_________________________
www.myphonetechs.com

Top
#33138 - 01/13/04 03:18 PM Re: Common Neutral Code ? 215.4 in 2002 NEC
DougW Offline
Member

Registered: 06/08/03
Posts: 1083
Loc: North Chicago, IL
You are correct. Thought that the interp. included shared neutrals in general.

Top
#33139 - 01/13/04 03:31 PM Re: Common Neutral Code ? 215.4 in 2002 NEC
Ryan_J Offline
Moderator

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
Its amazing how mis-interpreted that provision is.
_________________________
Ryan Jackson,
Salt Lake City

Top
#33140 - 01/13/04 04:25 PM Re: Common Neutral Code ? 215.4 in 2002 NEC
Roger Offline
Member

Registered: 05/18/02
Posts: 1779
Loc: N.C.
Rob, let's look at your question closely.

First of all 215 is for feeders so we will leave this section and go on to 225.7(B) which will allow you to put as many circuits as you want on a properly sized neutral. Yes this section is specific to "Outside Branch Circuits and Feeders" but there is nothing in any other section prohibiting it for other applications.

If you are using a neutral conductor the same size as the circuit conductors, then you could have a neutral common to both ends of a single winding, (transformer) or common to three windings connected in a wye or star configuration. This goes with Cpalm1's post

I know, I'm causing trouble.

Roger

[This message has been edited by Roger (edited 01-13-2004).]

Top
#33141 - 01/13/04 05:11 PM Re: Common Neutral Code ? 215.4 in 2002 NEC
wa2ise Offline
Member

Registered: 11/29/02
Posts: 771
Loc: Oradell NJ USA
Say that there were 4 15 amp circuits sharing one neutral. If 2 circuits come from one side of the supply, and the other two are fed by the other side, then can I use one neutral that is sized to take 30 amps (AWG 10 IIRC)? This would have to be in one conduit I would think.

Top
#33142 - 01/13/04 05:25 PM Re: Common Neutral Code ? 215.4 in 2002 NEC
Roger Offline
Member

Registered: 05/18/02
Posts: 1779
Loc: N.C.
Wa2ise, yes that would be allowed per 225.7(B)specificaly. Seems strange doesn't it.

Roger

Top
#33143 - 01/13/04 07:49 PM Re: Common Neutral Code ? 215.4 in 2002 NEC
Scott35 Offline

Broom Pusher and
Member

Registered: 10/19/00
Posts: 2724
Loc: Anaheim, CA. USA
Roger;

 Quote:

I know, I'm causing trouble.


Not even if you tried to!

Addressed things which are indeed very related to this scope.

I like the descriptions of Transformers, which basically caught my eye - and led to this reply!

To the original poster:

Although the idea of using an oversized Common Grounded Conductor for several multiwire circuits is compliant to the NEC, it still just sounds odd to me!
It works, and should be safe - if installed properly; it's only a "different" method, very much "unthought of" by many of us here - including myself!

Regardless of which option you choose - be sure to have a "Balance" of Ungrounded Conductors which are derrived from Breakers on "Opposite Polarity Points" in the Panel.
Simply, if you can measure 220-240 VAC across two Breakers, use these two circuits for a single multiwire circuit. Step down 1 space from that multiwire for the next one.

BTW: Per the term "Opposite Polarity Points", I use that term because "Opposite Phases" really does not apply to a 1Ø 3W system.

Talk about starting trouble

Scott35
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!