#329 - 01/16/01 09:57 AM Confirming properly grounded equipment
Harold Best Offline
Junior Member
Registered: 01/16/01
Posts: 2
Loc: Danville, KY, USA
I work in the safety department and we utilize a new equipment checklist for any new or altered equipment. One of the items on the checklist deals with the proper grounding of equipment. I have asked various electrical contractors to confirm that the equipment they have installed is properly grounded before I complete the checklist. Does anybody have any suggestions at to the best way to confirm that the equipment is properly grounded? What type of confirmation test should we require?
Top
Work Gear for Electricians and the Trades
#330 - 01/16/01 12:45 PM Re: Confirming properly grounded equipment
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
Harold;
the grounding requirements of article 250 in the NEC are many times pertinent to specific equipment. So you may need an answer for each individual situation.
Top
#331 - 01/16/01 01:50 PM Re: Confirming properly grounded equipment
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 3875
Loc: NY, USA
Harold,

Perhaps if you gave us more details on the types of equipment you are dealing with We would be better able to offer suggestions.


Cord and plug connected? - if so, are you referring to the grounding of the equipment itself or the circuit it is connected to?

What type of location is this equipment installed in? is it a Hazardous Location?
more details might help.

Bill
Top
#332 - 01/16/01 02:02 PM Re: Confirming properly grounded equipment
Harold Best Offline
Junior Member
Registered: 01/16/01
Posts: 2
Loc: Danville, KY, USA
Quote:
Originally posted by Bill Addiss:
Harold,

Perhaps if you gave us more details on the types of equipment you are dealing with We would be better able to offer suggestions.


Cord and plug connected? - if so, are you referring to the grounding of the equipment itself or the circuit it is connected to?

What type of location is this equipment installed in? is it a Hazardous Location?
more details might help.

Bill


This checklist is used for any new or altered equipment. The most recent items I have used the checklist on include: cardboard baler, dock locks, Landringer (puts plastic wrap around loads on pallets), production auxillary equipment, etc.

I assume you just have to look at the specific equipment and determine how the grounding should be confirmed (i.e. test with meter, etc.).
Top
#333 - 02/11/01 11:54 PM Re: Confirming properly grounded equipment
BR Offline
Junior Member
Registered: 02/12/01
Posts: 1
Loc: USA
The equipment installation should be inspected to meet the requirements of NEC 250. "Checking with a meter" will not tell you much if you use a multimeter. The ohmmeter section will only measure resistance, not impedance. You need to use an impedance tester such as a Tasco Inspector, ECCOS, Suretest, or GLIT if you want to measure inpedance.
Top
#334 - 02/13/01 04:40 PM Re: Confirming properly grounded equipment
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
BR;
May i ask which impedance tester you would recommend? I am in the market for one....
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
2 registered (Admin, sparkyinak), 74 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals